Re: Question about generator grounding - 2 chassis bonds going to different grounding poChrisOlson wrote: »So if you run separate PV- from each power source to each controller, and PV- and B- are really the same in the Classic, then they are all connected together anyway thru the same B- going to every controller
You're correct about the classic. Outback does it that way also. --vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Question about generator grounding - 2 chassis bonds going to different grounding po
And the three+ pole DC GFI only works for DC shorts on the PV array side of breaker (i.e., a DC PV short to earth that draws more than 1 amp) because the breaker only cuts off the PV source of power.So true. After the GFP trips, all neutral DC wiring can be hot and unfused with respect to ground.
There is a simple solution for one controller... use Outback's 3 pole GFP device to disconnect both PV pos and PV neg when a fault is detected.
For two controllers you would need a 5 pole GFP (one pole being the ground fault detector and the other 4 disconnect pos and neg from two arrays), but I don't think they make one with that many poles.
--vtMaps
If there is a DC to earth fault anywhere else in the system (battery to earth, inverter to earth, MPPT charge controller to earth, any other wiring fault to earth)--There is no other two pole breaker to stop those sources of power at all (i.e., short the battery + to earth, DC GFI does nothing to "interrupt" the source of the fault's power).
Just a big mess--There are a dozen major fault situations where DC GFI does not work or causes more problems than it fixes).
The only reason DC GFI even sort of works--There is a 1 amp fuse between DC Return and Earth Ground that stops current flow... But, in normal AC and DC wiring with single pole breakers/fuses, placing a fuse between return and safety ground is never a supported configuration (except in solar power systems). If you have a (now) floating power system, you need two pole ganged breakers on every power source to "safe" the system if there is a fault.
Which then would add costs (more breakers with slave trips) and--If there is ever a hot to earth fault anywhere in the DC power system--It kills power to the entire DC power system.
Just as bad as slaving the Main House Breaker to every breaker in the panel--Any fault kills the power to the whole home--killing power/lights everywhere in the home and making it very difficult for fault isolation.
When design larger Computer/communications systems, putting fuses in the return/safety ground leads would have made my job a lot easier--The customers a lot less safe and the systems much less reliable.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Question about generator grounding - 2 chassis bonds going to different grounding poAs I recall from posts years ago--The (then) Xantrex XW 60 amp MPPT controller put a current shunt the negative PV- lead to measure the current flow when doing MPPT calculations. So, for that controller--specifically, you cannot common bus the solar array PV- leads.
Ah. Never thought about that. If that's the case then I'll have to separate out the PV- on the array that's going to feed the XW-MPPT-60. Thanks for pointing that out, Bill, as I believe you're right on that point.
--
Chris -
Re: Question about generator grounding - 2 chassis bonds going to different grounding poChrisOlson wrote: »Ah. Never thought about that. If that's the case then I'll have to separate out the PV- on the array that's going to feed the XW-MPPT-60. Thanks for pointing that out, Bill, as I believe you're right on that point.
--
Chris
Xantrex and BlueSky controllers do not support common PV negative. Don't remember where I got that from, Think it was the Midnite Solar combiner box manual. I assumed it was over the GFCI because the manual wanted you to keep it in for only one controller. -
Re: Question about generator grounding - 2 chassis bonds going to different grounding poChrisOlson wrote: »It's interesting that you ask that question - I did some re-wiring on my solar arrays and high voltage DC bus over the weekend in preparation for installing my XW-MPPT-60 to take some of the peak load off my Classic 150. And since I'm installing dual controllers for the solar, I went to the RE dealer where I get most of my equipment on Saturday morning and bought 1.5kW more panels so I have enough installed capacity (7.5 kW) to run both controllers at 90% of their rated output capacity (total 130 amps).
I'm going to put in the additional panels today on the house roof (it's cooler here and cloudy today so I can work on the roof without wrecking the shingles) and get them wired into the combiner.
Then I have to review the -60-150 manual myself to figure out the grounding and ground fault protection for it when I install it.
--
Chris
James hated everything about where Xantrex put the grounding terminal and GFCI fuse in their charge controller. You will need some mighty fine fingers to get a #6 in there (Also, southwire THHN is very stiff wire).
Categories
- All Categories
- 233 Forum & Website
- 141 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 199 Solar Information links & sources, event announcements
- 900 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 429 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 624 Energy Use & Conservation
- 623 Discussion Forums/Café
- 315 In the Weeds--Member's Choice
- 75 Construction
- 125 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed