Intelligent Load Shedding with Xantrex XW System
aj164
Solar Expert Posts: 122 ✭✭✭
I think it would be _possible_, but how well would load-shedding work on a Xantrex XW?
Let's say you have two critical loads panels. In one panel, you have a contactor, which, when activated, disconnects that panel from the load. On that panel, you have the less-important, larger loads, such as water heating or HVAC.
To control the contactor, you use the XW inverter auxiliary digital output. You set the output to trigger on battery voltage. When it drops below your set threshold, the contactor is energized, disconnecting part of the load.
Question 1: When the load drops significantly, battery voltage will probably come back up. Would this cause "hunting", where the load gets switched in and out continuously with fluctuating battery voltage? I know there is a trigger delay and a clear delay setting, which could help some.
Q2: If you have multiple XW inverters, do you get multiple, independently-configurable auxiliary outputs?
Thanks,
AJ
Thanks,
AJ
Re: Intelligent Load Shedding with Xantrex XW System
I can answer the first question, Yes the battery voltage would climb with less load but you can program the XW aux output for trigger level, trigger delay, clear level and clear delay. With these settings, you can set up some hysteresis to minimize the kerchunking.
ETA: Be real careful what you connect to the aux output, it isn't very well protected and you can blow it up with a transient, you need a good relay driver between the aux and the contactor. -
In addition to the XW inverters, each charge controller has an auxiliary output. I'm still hoping for confirmation that these can all be independently configured.
-AJ -
Re: Intelligent Load Shedding with Xantrex XW SystemETA: Be real careful what you connect to the aux output, it isn't very well protected and you can blow it up with a transient, you need a good relay driver between the aux and the contactor.
How about a solid-state AC relay? -
You can control all of the levels I mentioned (in my previous post) for both the inverter and the SCC AUX outputs the SCC has a few more options as well such as voltage levels. If you connect anything to this output, I would make very sure with a scope that it could not produce a transient on the aux output. I clamped the bejesus out of my relay driver and it still managed to blow up the AUX output on one of my SCC's. I even sent my schematic to XW tech support and they said it shouldn't have blown up but it did. Just be careful, it seems like it is easy to blow it up.In addition to the XW inverters, each charge controller has an auxiliary output. I'm still hoping for confirmation that these can all be independently configured.
-AJ -
I've been driving this AC SSR with the AUX output on our XW inverter since we installed the inverter, with no problems at all -
Re: Intelligent Load Shedding with Xantrex XW SystemHow about a solid-state AC relay?
You need to read the specs on the relay. AUX on XW6048 can source 250mA (3W). I use it to run a 2.4W battery fan, and it works fine. Higher loads may damage it.
AUX on SCC is less powerful. You can find its specs in the manual. -
I'm pretty sure the 12V output on pins 1 & 2 is internally protected from over current. There is not a relay in there for that - it is electronically controlled and will turn it off if the current exceeds .25 amp. The reason I think that is because I tried it with a mechanical relay that draws more power for the coil than what the AUX can supply on pins 1 & 2. It initially engaged the relay, but then kicked out for awhile before it tried it again and kicked out again. It didn't appear to do anything bad to the AUX output in the inverter, as it still works fine with the SSR that I showed the picture of.
Chris -
Re: Intelligent Load Shedding with Xantrex XW SystemChrisOlson wrote: »I'm pretty sure the 12V output on pins 1 & 2 is internally protected from over current. There is not a relay in there for that - it is electronically controlled and will turn it off if the current exceeds .25 amp. The reason I think that is because I tried it with a mechanical relay that draws more power for the coil than what the AUX can supply on pins 1 & 2. It initially engaged the relay, but then kicked out for awhile before it tried it again and kicked out again. It didn't appear to do anything bad to the AUX output in the inverter, as it still works fine with the SSR that I showed the picture of.
That's a definite possibility. In the docs they say fuse is not required, so it should be able to withstand dead short without damage. I installed 0.5A fuse anyway
Danger Will Robinson! You are very lucky, the inductive kick from your original trial could have very well done in your AUX output. The output is indeed protected for over current but in my experience is not well protected from a transient overvoltage condition. It should have no trouble driving the LED in a SSR but relay coils require a driver to isolate things.ChrisOlson wrote: »I'm pretty sure the 12V output on pins 1 & 2 is internally protected from over current. There is not a relay in there for that - it is electronically controlled and will turn it off if the current exceeds .25 amp. The reason I think that is because I tried it with a mechanical relay that draws more power for the coil than what the AUX can supply on pins 1 & 2. It initially engaged the relay, but then kicked out for awhile before it tried it again and kicked out again. It didn't appear to do anything bad to the AUX output in the inverter, as it still works fine with the SSR that I showed the picture of.
Chris -
Re: Intelligent Load Shedding with Xantrex XW SystemIt should have no trouble driving the LED in a SSR but relay coils require a driver to isolate things.
It works well with my 2.4W battery fan, which is an inductive load too. It is designed to operate relays, so it should have some sort of protection against inductive load. I cannot tell for sure, of course. -
I figure it's under warranty. If it blows they can fix it 8)
Chris -
Sounds like it has a "Polyswitch" or PTC (positive temperature coefficient) resistor on the output.
They are not perfect fuses--But if used correctly, it saves having to pop open a device and soldering a new fuse or repairing a trace.
I sure hope they have a diode clamp on the output of their "switch" to prevent an inductive kickback from putting a couple hundred volts across the switching element.
Re: Intelligent Load Shedding with Xantrex XW SystemSounds like it has a "Polyswitch" or PTC (positive temperature coefficient) resistor on the output.
It acts like the same thing the Classic 150 controllers have on their AUX output. Ryan told me it's a "self-healing" fuse and the one in the Classic will handle 200 mA.
Chris