Just at the local Electrical supplier looking at distribution boxes and noted that the:
100 A 20 slot ,
125 A 32 slot and
200 A 40 Slot boxes
all use the same ground buss bar part # PK 9 GTA therefore they all are 200 A rated bars8)8)
The next size up (250A??) uses a different part #.
100 A 20 slot ,
125 A 32 slot and
200 A 40 Slot boxes
all use the same ground buss bar part # PK 9 GTA therefore they all are 200 A rated bars8)8)
The next size up (250A??) uses a different part #.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Comments
-
Re: Square D buss bars
Grounding bus bar, or Hot bus bar?
Since ground ordinarily carries no current it doesn't really matter what its rating is.
It's the bars for Hot and Neutral that make the difference. -
Re: Square D buss bars
I will check that out next time I am there.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Square D buss bars
Many panels have a general purpose bus bar that can be an isolated "white wire" bus, or with a ground wire/screw can also be the main panel ground bus too. So, it is very possible and likely that such a bus would have to be rated for the maximum current allowed by the main power bus bars too.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Square D buss bars
I was thinking that just because the same grounding bar is used in the 100 as the 200 doesn't mean either is actually rated for 200 Amps. Ground circuitry only has to carry current long enough to trip breakers, not continuously. -
Re: Square D buss barsCariboocoot wrote: »Grounding bus bar, or Hot bus bar?
Since ground ordinarily carries no current it doesn't really matter what its rating is.
It's the bars for Hot and Neutral that make the difference.
Exactly right!
The ground bus is more likely sized to match the maximum number of breakers the panel will hold, rather than the listed amperage.
Not conclusive evidence, but the Square D load centers in the QO (R) and Homeline (R) families divide into two groups:
100-125 amps and 150-225 amps. That suggests strongly to me that the 100 and 125 amp units MIGHT both have 125 Amp busses while the 150-225 units MIGHT have 225 amp busses.
The only ways to tell for sure are to ask Schneider or to look at the part number(s) on the buss assemblies themselves.SMA SB 3000, old BP panels. -
Re: Square D buss bars
you guys are overlooking the obvious here and that is the number of slots. a 200a buss will be required to have more connections as there are more breaker slots available. they are more than likely the same, but differing lengths with more or less positions. -
Re: Square D buss barsyou guys are overlooking the obvious here and that is the number of slots. a 200a buss will be required to have more connections as there are more breaker slots available. they are more than likely the same, but differing lengths with more or less positions.
I am actually not overlooking it, but there are numerous sizes (slot numbers) available in the 200 amp capacity. So the part number may vary even though the current capacity stays the same. To make use of the part number information, you would have definitely need to compare panels with the same length busses.
The main breaker and main lug wire sizes are in two groups and the breaker to lug conversion parts which attach to the end of the bus are also available in exactly two part numbers, one for 100-125 and one for 150 -225.
Still only circumstantial. But given the cost of getting parts qualified, they have a good motivation to use common parts.SMA SB 3000, old BP panels.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed