Battery Choices
larrybc1
Solar Expert Posts: 44 ✭
Hi,
Need some help on deciding the best battery to go with..I am in the Philippines so dont have a lot of choice on batteries--No Rolls Surrette..Trojan was the best I could find.
My system is 25 ==210 watt panels..loads initially 9000-10,000 Watt Hours per day--but it is a beach resort and I want a bigger system in case of expansion I will be able to handle the increased loads.
Battery choices:
1. Trojan Premium Line L16RE-2V--1110 AH/20 hr rate..$400 each..need 24 batteries= $9600
2. Trojan Industrial Line IND17-6V--897 Ah/20hr...$952 each..need 8 batteries= $7616
3. Trojan Industrial Line IND23-4V--1233AH/20hr..$906 each..need 12 batteries= $10872
trying to keep just 1 string of batteries..Been told that the Industrial Line will last much longer..
thks Larry
Need some help on deciding the best battery to go with..I am in the Philippines so dont have a lot of choice on batteries--No Rolls Surrette..Trojan was the best I could find.
My system is 25 ==210 watt panels..loads initially 9000-10,000 Watt Hours per day--but it is a beach resort and I want a bigger system in case of expansion I will be able to handle the increased loads.
Battery choices:
1. Trojan Premium Line L16RE-2V--1110 AH/20 hr rate..$400 each..need 24 batteries= $9600
2. Trojan Industrial Line IND17-6V--897 Ah/20hr...$952 each..need 8 batteries= $7616
3. Trojan Industrial Line IND23-4V--1233AH/20hr..$906 each..need 12 batteries= $10872
trying to keep just 1 string of batteries..Been told that the Industrial Line will last much longer..
thks Larry
Comments
-
Re: Battery Choices
Well 10kW hours on a 48 Volt system is about 208 Amp hours. Keeping the DOD down to 25% would be 834 Amp hours minimum.
That array (5250 Watts) should be able to produce 84 Amps on a 48 Volt system, which would support 840 Amp hours (above battery capacity fine).
For 1110 Amp hours that's a 7.5% peak charge rate.
For 897 Amp hours that's a 9.3% peak charge rate.
For 1233 Amp hours that's a 6.8% peak charge rate.
Looks to me like over-all the IND17-6V is the best choice. -
Re: Battery ChoicesCariboocoot wrote: »Well 10kW hours on a 48 Volt system is about 208 Amp hours. Keeping the DOD down to 25% would be 834 Amp hours minimum.
That array (5250 Watts) should be able to produce 84 Amps on a 48 Volt system, which would support 840 Amp hours (above battery capacity fine).
For 1110 Amp hours that's a 7.5% peak charge rate.
For 897 Amp hours that's a 9.3% peak charge rate.
For 1233 Amp hours that's a 6.8% peak charge rate.
Looks to me like over-all the IND17-6V is the best choice.
thks for the info..I have the Outback FM80 charge controllers..I was looking at the peak efficiency chart and it shows the best efficiency at around 68 volts input from the panels..with my array setup ( 2x5 and 3x5) i will have 92 volts going to the charge controller and it shows an efficiency drop of around 2%..istill around 95% efficient..is that anything to worry about? thks -
Re: Battery Choicesthks for the info..I have the Outback FM80 charge controllers..I was looking at the peak efficiency chart and it shows the best efficiency at around 68 volts input from the panels..with my array setup ( 2x5 and 3x5) i will have 92 volts going to the charge controller and it shows an efficiency drop of around 2%..istill around 95% efficient..is that anything to worry about? thks
No, not really. That efficiency drop will occur only at full power and only if the controller chooses to load the array in that manner. It may choose a completely different current * Voltage setting than Imp * Vmp at any given time depending on what it 'thinks' is best.
The FM80's output current is limited to 80 Amps, so any current possible above that will not be available to charge the batteries. Another reason to not got with a larger bank as it will further decrease the peak charge rate (by a small amount). -
Re: Battery Choices
I would consider a forklift battery like a Crown (NAWS carries them) or something along the lines of 2 volt cells. The Trojan L16RE is basically an L16 with the 3 cells wired in parallel so you already have 3 strings when you buy them. The forklift cells are pretty forgiving but do have a little more self-discharge so would require a bit more power, but tend to last a very long time. If a forklift-type 2 volt cell goes bad there are used ones available to put back so the pack can be used more. Not so much with the L16 types. Shipping is so expensive for you it doesn't make sense to go with anything that won't last a very long time, so I would factor that in.
Good luck and let us know how it went.
Skip12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Re: Battery ChoicesI would consider a forklift battery like a Crown (NAWS carries them) or something along the lines of 2 volt cells. The Trojan L16RE is basically an L16 with the 3 cells wired in parallel so you already have 3 strings when you buy them. The forklift cells are pretty forgiving but do have a little more self-discharge so would require a bit more power, but tend to last a very long time. If a forklift-type 2 volt cell goes bad there are used ones available to put back so the pack can be used more. Not so much with the L16 types. Shipping is so expensive for you it doesn't make sense to go with anything that won't last a very long time, so I would factor that in.
Good luck and let us know how it went.
Skip
Hi skip,
will look for some forklift batteries in Manila..should have some there..So the Trojan 2 Volt is not so good? thks larry -
Re: Battery Choices
In batteries, the less strings the better and the 2 volt Trojan L16RE is 3 of the 2 volt cells in parallel so you're already dealing with 3 strings. It is the same thing as getting 24 of the L16's at 6 volts each and making 3 parallel strings, just that the hookups are done inside the jar. Not the best way to go and not known to last near as long as the 2 volt cells that are large like the Crown type. Here's a link to the NAWS ones, but like you said, check out the local fare. http://www.solar-electric.com/2voltbatteries.html
Good luck,
Skip12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Re: Battery Choices
Yes the 2 Volt Trojans are the 6 Volts with the cells paralleled instead of connected in series.
Yes they are less than ideal for a 2 Volt cell because you have three reservoirs to check instead of one.
No they do not present the parallel string problem found with multiple batteries because the parallel connections are fixed and internal to the battery; not much different from constructing one larger cell in electrical terms. The main problem is the 3X as many reservoirs.
In any case they aren't a good choice here.
The forklift batteries may not be either; they are monolithic, which means heavy and difficult to manage. Otherwise a fine source of power. -
Re: Battery Choices
actually, if you look at the sunxtender l16 lineup you'll notice the same pattern so i believe the 2v l16 is also using the 3 cells paralleled internally. a few of their other 2v batteries are similar as other 6v versions, but with the cells wired for parallel internally. in the case of agm batteries though you can't check on the individual cells by specific gravity so i would prefer in a case like that to take the risk of 3 parallel strings using the 6v batteries that you could at least isolate the batteries and check their individual voltages.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed