Hi Rngr,
I did post this previously in this Thread, "Please use the settings recommended by Trojan, at least until you do get the Hydrometer. I do not want to pick, but a few tenths of a volt does make a difference, so, IMHO, your settings are not really that close to the recommendation".
So, Please, Please DO reset the Absob voltage to exactly what is specified by Trojan, 59. 2 volts. Later if you are not using much of your battery's capacity, you might be able to reduce this setting a bit. However, as we move toward Winter, many of us become "Opportunity Charger" types. This is when we try to get as much charge from PV as we can, and then it is OK to jack up the Absorption V a bit more. Of course, this higher V only works when the charger gets into the absorption stage.
Also, in my opinion, the EQ voltage should be temperature Compensated. There is a place in the Classic's Menus to enable that, and believe that you should do that. Some inverters do not compensate EQ voltages, so if the bank temp is very far from the speced temps for the batts (think it is 80 degrees F for Trojan), you might need to temp comp the inverter EQ voltage manually by adjusting the EQ voltage a bit.
And, am certain that you are using the Batt Temp Sensor on the Classics AND on the Inverter as well (?), this is very important.
So please DO increase the Abosorption voltage settings on the inverter and Classics to that recommended by Trojan -- 59.2. Then you might wait for a few days, monitor the SGs, and then decide if the A.sorb time should be changed. The high-ish Vabs needs to be set this high if for no other reason that that is what the mfg says, and also because these batts have fairly high SG electrolyte.
Please rinse your Hydormeter after each measuring session, several times, using distilled water -- this is important.
There is a lot to digest in this Thread, good luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: Ensuring I am doing the right thing
Vic,
I re-read the owners manual and Trojans web site and there is a a little twist: It says"
Daily Charge= 59.2v
Absorbtion charge for RE-Applications= 56.4-58.8v
So I think the 58.8v I have set for Absorb would be correct for this application? Would you/everyone agree? -
Re: Ensuring I am doing the right thingI re-read the owners manual and Trojans web site and there is a a little twist: It says
Daily Charge= 59.2v
Absorbtion charge for RE-Applications= 56.4-58.8v
So I think the 58.8v I have set for Absorb would be correct for this application? Would you/everyone agree?
I would go with Trojan's recommendation for RE. But, since that is a lower voltage, I would also do a short equalization every week. Many battery manufacturers recommend high voltages for their 'daily' charge, but this is in the context of deeply discharged batteries that need to be fully charged in a hurry (before the next shift). Doing daily high voltages may be hard on a battery that is only discharged 15-20% every day.
Forum member 'Stephendv' has written about some charging profiles for some european RE equipment that uses a daily lower voltage absorb and once a week does a higher voltage finishing charge. It makes sense to me and I might lowering the daily charge voltage on my system (I'm at 29.6 volt daily absorb which would be equivalent to 59.2 on your system).
Another approach that some folks take is to use lower voltages in the summer (when you have more hours of absorb time) and higher voltages in the winter (when there are less hours available).
Bottom line is that long hours of high voltages are bad for the battery.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Ensuring I am doing the right thing
Hi Rnge..
Thanks for the added info regarding RE Vabs settings.
There are several ways to increase the SGs of your battery bank. Absorption Time, Voltage, and EQ Time and Voltage.
Increasing the Absorb time would be the first to try. But, if , for example, you do not have enough time in the Solar day to get the charging done, then one can increase the Vabs. The higher V will cause a bit more water to be used, but getting the SGs up to the target value speced by Trojan is important.
Your bank is young. Just get those SGs up to 1.277-ish, and then you can begin tweaking the Absorption time and Voltage, and calibrating the Batt Mon. But, the batteries are not getting fully recharged, and this needs to be remedied as soon as at all possible. Your batteries are a member of your family. They are asking for attention, so please get the SGs up to 1.277-ish NOW. It IS good that you are paying attention, and asking questions now.
Good Luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: Ensuring I am doing the right thing
Thanks All... I am determined to NOT be one of those who ruin their first set of batteries! -
Re: Ensuring I am doing the right thingThanks All... I am determined to NOT be one of those who ruin their first set of batteries!
Take your time,if in doubt write it down. -
Re: Ensuring I am doing the right thing
Hi Rngr..
I would crank up the Absorb voltage to 59.2 or so AND increase Absorb time as well, until you can get the SGs up to spec. Then you can quite possibly reset the V a bit lower, but only if you can complete the Absorption stage in the time that you have enough PV input to get into Float. You know your local weather, I do not!
To me, the first 25-50 cycles of the bank increases the CAPACITY of the bank. The SG should get the 1.277 target on most of these cycles. This is the way tha all of the banks that I've had/monitored have been, although, none have been Trojans. But, would be surprised if Trojans behaved differently.
vtmaps, yes the "lower Summer Vabsorb, higher in Winter" is the Opportunity Charge that referred to above. YES, many hours of too high charge V is bad, chronic undercharging is considerably worse. IMHO.
Rngr, it IS very good that you are paying attention to your system/batteries, and asking questions, when the system is young, not when the "lights go out"! Good Luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed