12V load on a 48V system
awade
Registered Users Posts: 14 ✭
I learned so much from reading this forum but I finally had to join because I've had this burning question that I can't seem to resolve. Thanks in advance for any answers you can offer.
I have a 48V system with sixteen 415ah L16's an Outback inverter and charge controller. I've tried various water pumps of various voltages and currents over the years and they all seem to fail relatively quickly. The work horse pumps that I've found to be the most reliable over time are the small 12V RV pumps like the Shurflo 2088-422-444 (3.5A at 12V). Problem is, how to use the pump with the system.
For the last year, as an experiment, I wired the pump direct to two of the 6V batteries within the 48V configuration, thus pulling 12V. It's been working perfectly, perhaps because of the low amperage, and those two batteries don't seem any worse off than the others. In fact, when all loads and charges are off, they seem to have slightly higher state of charge.
That said, I've read and heard that you should never wire a 12V load directly into a 48V battery bank so I am searching for a solution.
Short of setting up a standalone 12V system just for a single pump, I've considered using 48VDC to 12VDC converter made for golf carts but I don't know how efficient they are.
Samlex makes a 48V to 12V converter that is more expensive but may be more efficient, or maybe not. I found it here: http://www.iloveitsolar.com/catalog/i412.html
Also, someone recommended using the Morningstar Sunsaver 15A MPPT as a 48V-12V converter since it can handled higher input but that sounds like overkill.
Early on, I had a 12V charger running off the AC inverter, which was servicing a 12V battery for the pump. It worked but 48VDC to 120AC to 12VDC to seemed ridiculous. Or is it?
Any elegant solutions out there? Your insights would be greatly appreciated.
Thanks!
I have a 48V system with sixteen 415ah L16's an Outback inverter and charge controller. I've tried various water pumps of various voltages and currents over the years and they all seem to fail relatively quickly. The work horse pumps that I've found to be the most reliable over time are the small 12V RV pumps like the Shurflo 2088-422-444 (3.5A at 12V). Problem is, how to use the pump with the system.
For the last year, as an experiment, I wired the pump direct to two of the 6V batteries within the 48V configuration, thus pulling 12V. It's been working perfectly, perhaps because of the low amperage, and those two batteries don't seem any worse off than the others. In fact, when all loads and charges are off, they seem to have slightly higher state of charge.
That said, I've read and heard that you should never wire a 12V load directly into a 48V battery bank so I am searching for a solution.
Short of setting up a standalone 12V system just for a single pump, I've considered using 48VDC to 12VDC converter made for golf carts but I don't know how efficient they are.
Samlex makes a 48V to 12V converter that is more expensive but may be more efficient, or maybe not. I found it here: http://www.iloveitsolar.com/catalog/i412.html
Also, someone recommended using the Morningstar Sunsaver 15A MPPT as a 48V-12V converter since it can handled higher input but that sounds like overkill.
Early on, I had a 12V charger running off the AC inverter, which was servicing a 12V battery for the pump. It worked but 48VDC to 120AC to 12VDC to seemed ridiculous. Or is it?
Any elegant solutions out there? Your insights would be greatly appreciated.
Thanks!
Comments
-
Re: 12V load on a 48V system
Welcome to the forum.
Using a separate 12 Volt system recharged from the 48 might be electrically inefficient as you say, but it can be a lot more practical in terms of expense than buying a converter.
Drawing off one section of the 48 Volt bank, even with a small drain, will imbalance the system. This will not show up right away, but instead will manifest itself as the batteries with extra use failing before the others.
You might even just get a whole separate small system to support the pump, as it probably would not need a large battery and associated panel & controller. -
Re: 12V load on a 48V system
Thanks for your quick response Cariboocoot,
Are you suggesting that the Sunsaver controller option is viable as a way to balance the 12V load over the 48V battery bank? If so, would I need a separate 12V battery between the controller and the pump or can I connect the pump directly to the controller without a battery.
Seems that even a charge controller or a converter would still be less expensive than setting up a new 12V system from scratch. -
Re: 12V load on a 48V system
using the 120vac inverted power to operate a 3 stage charger to a dedicated 12v battery may be one way and would keep the main battery bank operating in balance. the 48v-12v converter is far more efficient and skips wasteful steps and costs far less than all of the components needed for a dedicated battery with ac charger from an inverter. sometimes people have some of the components to enable the first method, but the dc to dc converter is best imho. -
Re: 12V load on a 48V system
Hi Niel,
Yeah, finding the most efficient converter might be best. Hopefully less maintenance than a separate system too. I've got about as much as I can handle, and I'm hoping to find a solid, long term solution.
I wonder, if my total 12V load is 3.5 amps, would it be more efficient to go with a small 5-10 amp converter or will a larger unit provide more efficiency through less resistance or better heat management, or just better durability? -
Re: 12V load on a 48V systemThanks for your quick response Cariboocoot,
Are you suggesting that the Sunsaver controller option is viable as a way to balance the 12V load over the 48V battery bank? If so, would I need a separate 12V battery between the controller and the pump or can I connect the pump directly to the controller without a battery.
Seems that even a charge controller or a converter would still be less expensive than setting up a new 12V system from scratch.
Absolutely must have a separate 12 Volt battery.
But considering the price of the MS 15 MPPT, using a small PWM charge controller and its own panel may be a more cost-effective option. It depends on how much pump power you need and what kind of bargains you can find. -
Re: 12V load on a 48V system
Are you aware that shurflo makes the 2088 series pump in other voltages, including 120 V AC? --vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: 12V load on a 48V system
Hi vtmaps,
Thanks for the thought. Yeah I am aware of the 120V AC version of the shurflo pump and have tried them twice. I wish I could say I had a good experience but both started running down, over heating or yielding less pressure after about 6-9 months of regular use. Not sure why but the 12V version has been providing solid service in both our house and our greenhouse with no signs of overheating and providing excellent pressure despite pushing through multiple stages of filtration. The greenhouse 12V pump has been working daily for 4 years with no signs of trouble. It's been running on an old truck battery tied to a 20 watt panel. Still going strong, knock on wood. -
Re: 12V load on a 48V system
I found a $20 48V to 12V converter and it's working great so far. Thanks for the input. -
Re: 12V load on a 48V system
Sounds like he's already found a converter, but others might find this info useful.
I bought a 25 Amp 48V to 12V DC-DC converter (commonly called a reducer) for $45. Works great. Pics and details of my testing here: http://www.buggiesgonewild.com/electric-ezgo/70417-48v-dc-dc-converter.html
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed