What size cable to use battery to Inverter?
westbranch
Solar Expert Posts: 5,183 ✭✭✭✭
I did some pricing of welding cable today and found some new ‘old’ stock OO at a great price, $12.15 / meter ($3.68/ft). It’s 20% less than elsewhere and only 5% more than the O size.
Got me thinking about just what size I really will need between the 24V BB and the 1500W Inverter. The load will be ~62.5 A (50A @ 30V to 71.5A @21V). Surge is 3000W 125A. (the manual calls for #4 ga wire and a 100A) fuse.
Using the No Outage voltage drop calculator, for 24V, 72A, 75*C, 8 feet one way, Copper wire,
I get with:
4 ga. 1.5 % drop
2 ga. .9 % drop
1 ga. .7 % drop
O ga. .6 % drop
OO ga. .5 % drop
All of these are ‘acceptable losses’, as the total line losses from PV to inverter remain below 3.75% @ 4 ga, 2.75% @ OO ga., but how does one do a cost/benefit analysis on these numbers?
From what I read, 2 ga. is borderline for Amps,(72), thus I need to use O ga, minimum for a 30% ampacity buffer. Then, considering I might want to eventually go to a larger 2000W inverter, (manual calls for #O wire with 125A fuse) I am leaning towards using OO ga. BB to inverter.
Do I have this figured out correctly?
Am I being too cautious/overestimated?
Got me thinking about just what size I really will need between the 24V BB and the 1500W Inverter. The load will be ~62.5 A (50A @ 30V to 71.5A @21V). Surge is 3000W 125A. (the manual calls for #4 ga wire and a 100A) fuse.
Using the No Outage voltage drop calculator, for 24V, 72A, 75*C, 8 feet one way, Copper wire,
I get with:
4 ga. 1.5 % drop
2 ga. .9 % drop
1 ga. .7 % drop
O ga. .6 % drop
OO ga. .5 % drop
All of these are ‘acceptable losses’, as the total line losses from PV to inverter remain below 3.75% @ 4 ga, 2.75% @ OO ga., but how does one do a cost/benefit analysis on these numbers?
From what I read, 2 ga. is borderline for Amps,(72), thus I need to use O ga, minimum for a 30% ampacity buffer. Then, considering I might want to eventually go to a larger 2000W inverter, (manual calls for #O wire with 125A fuse) I am leaning towards using OO ga. BB to inverter.
Do I have this figured out correctly?
Am I being too cautious/overestimated?
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Comments
-
Re: What size cable to use battery to Inverter?
the figures are pretty close to what you figure them to be. the 2/0 may be overkill, but it will take out a large problem area for v drops even with an expansion to your proposed 2kw. wire won't ever be cheap and will no doubt go up in years to come so i'd take advantage of it.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 885 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed