Trimetric setpoint for 12V system
intel415
Solar Expert Posts: 31 ✭
Hello guys,
For those who owns a trimetric please give me some help please. I got my trimetric today, but still waiting for the 100A shunt to come tomorrow, so i can put everything together. I have read the manual for a 12V system flooded batteries P1 Charged setpoint voltage is 14.3, P3 is the battery capacity Ah, i have 2 t-105 rated at 225AH (20 hours) do i need to divide it by 20? or just leave it as 225AH? according to the manual P2 setpoint amp is dtermined by taking 2% of P3 AH value or (multiply P3 value by 2 divide by 100%). If i use 225AH i get 4.5
So i want to know if these numbers are right for 12V 2 t-105 (225AH) connected in series
P1 "charged" setpoint voltage = 14.3
P2 "charged" setpoint amp = 4.3
P3 "battery capacity" amp-hours = 225
Thanks.
For those who owns a trimetric please give me some help please. I got my trimetric today, but still waiting for the 100A shunt to come tomorrow, so i can put everything together. I have read the manual for a 12V system flooded batteries P1 Charged setpoint voltage is 14.3, P3 is the battery capacity Ah, i have 2 t-105 rated at 225AH (20 hours) do i need to divide it by 20? or just leave it as 225AH? according to the manual P2 setpoint amp is dtermined by taking 2% of P3 AH value or (multiply P3 value by 2 divide by 100%). If i use 225AH i get 4.5
So i want to know if these numbers are right for 12V 2 t-105 (225AH) connected in series
P1 "charged" setpoint voltage = 14.3
P2 "charged" setpoint amp = 4.3
P3 "battery capacity" amp-hours = 225
Thanks.
Comments
-
Re: Trimetric setpoint for 12V systemSo i want to know if these numbers are right for 12V 2 t-105 (225AH) connected in series
P1 "charged" setpoint voltage = 14.3
P2 "charged" setpoint amp = 4.3
P3 "battery capacity" amp-hours = 225
Finish amps at 2% of rated capacity would be:
P2 "charged" setpoint amp = 4.5
I'm guessing it was just a typo since you had it at the end of the first paragraph.;)
And yea, you want to use 2% (P3 x 2 / 100%) of the total capacity not just the C20 rate (total capacity / 20 hrs).
Alex Aragon -
Re: Trimetric setpoint for 12V system
yes it is a typo lol
so i need to use p2 charged setpoint amp = 4.5A right?
thanks agian.
Thanks. -
Re: Trimetric setpoint for 12V systemyes it is a typo lol
so i need to use p2 charged setpoint amp = 4.5A right?
Yep.
DOn't forget that the "end amps" can change over time with tempurature and health of the battery. Bulk charge settings can change if your charger has temp comp.
Once you have the meter set, you should make it a habit to confirm the SOC readings with voltage and amps. They can get off track. I.E. if the sun is down and the SOC show 100% but the voltage is 12.1 with no loads, you should be very suspicious.
Alex -
Re: Trimetric setpoint for 12V system
Thanks Alex,
I also emailed Bargart engineering, they recommended to round 4.5 to 4 or 5. Interesting point you point out about no sun condition never though of that lol i will keep an eye on it.
Thanks.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed