Question on float voltage
techntrek
Solar Expert Posts: 1,372 ✭✭✭
System recap - (16) 12 volt FLA in series, 115 amps 20-hour rating, attached to a double-conversion UPS. Emergency duty, carries most 120 volt loads until my big genset starts up, and for long outages it was the primary power source up to 18 hours per day (rare). Batts are about 3 1/2 years old.
My old UPS floated at 226 volts, or about 14.1 volts per battery. High but I didn't have much choice since it wasn't adjustable. Watering was critical before the 6-month point, I was pushing my luck if I went beyond that. The upside was I had a few more amps available during a long outage. Downside other than heavy water useage is it probably took some life off of the batts.
New UPS is fully adjustable. I've already moved the float point from 13.6 to 13.8. I'm starting to rethink that since some sources say long-term/emergency float should be 13-13.2. Now that I have the Prius available as a power source for the UPS my strategy has changed - the batts are only needed until genset startup, or for shorter outages if I don't need the big genset. For long-term outages the Prius will be in use up to 20 hours per day.
So now the goal for the batts isn't more amps available, but long life. What is your recommendation for the float voltage? I assume I should go down to 13.2... (@ room temperature) No manufacturer specs available, if someone was going to ask.
My old UPS floated at 226 volts, or about 14.1 volts per battery. High but I didn't have much choice since it wasn't adjustable. Watering was critical before the 6-month point, I was pushing my luck if I went beyond that. The upside was I had a few more amps available during a long outage. Downside other than heavy water useage is it probably took some life off of the batts.
New UPS is fully adjustable. I've already moved the float point from 13.6 to 13.8. I'm starting to rethink that since some sources say long-term/emergency float should be 13-13.2. Now that I have the Prius available as a power source for the UPS my strategy has changed - the batts are only needed until genset startup, or for shorter outages if I don't need the big genset. For long-term outages the Prius will be in use up to 20 hours per day.
So now the goal for the batts isn't more amps available, but long life. What is your recommendation for the float voltage? I assume I should go down to 13.2... (@ room temperature) No manufacturer specs available, if someone was going to ask.
4.5 kw APC UPS powered by a Prius, 12 kw Generac, Honda EU3000is
Comments
-
Re: Question on float voltage
techntrek,
this is really determined by the battery manufacturer as to the best float voltage. it is a minor charge meant to offset self discharge. having it a bit higher probably won't hurt it, but will create more maintenance. it won't be more charged than the normal float setting as when a battery is fully charged it just doesn't accept more and will dissipate the excess as heat. -
Re: Question on float voltage
Well, I've now read a dozen or so articles and FAQs which quote numbers from 13.0 to 13.8. I might bump it back down a notch or two.4.5 kw APC UPS powered by a Prius, 12 kw Generac, Honda EU3000is -
Re: Question on float voltage
i don't think it would be below 13.2v and my feel is it is most likely around 13.4v to 13.8v, but as i said it's depending on who makes them.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed