Another weird setup
lazza
Solar Expert Posts: 336 ✭✭✭
HI.
We've just visited an existing installation, where the owner has cleverly put 2 grid-tie Kyocera panels similar to the following: http://www.kyocerasolar.com/assets/001/5129.pdf .... connected to a 24V charge controller and 24V battery sytem.
The Vmp is around 26V in STC and only 24V in NOCT, and what I cant understand is that in theory the system shouldnt work, yet it seems to be charging his batteries somehow, maybe not optimally, but charging it is.
Can anyone enlighten me on how this may be happening?
thanks
We've just visited an existing installation, where the owner has cleverly put 2 grid-tie Kyocera panels similar to the following: http://www.kyocerasolar.com/assets/001/5129.pdf .... connected to a 24V charge controller and 24V battery sytem.
The Vmp is around 26V in STC and only 24V in NOCT, and what I cant understand is that in theory the system shouldnt work, yet it seems to be charging his batteries somehow, maybe not optimally, but charging it is.
Can anyone enlighten me on how this may be happening?
thanks
Comments
-
Re: Another weird setup
It turns out that the peak Power/Current curve is fairly flat... So while Vmp~24 volts, if you look at a generic (Suntech) panel I/V/P curve (PDF), if you are willing to accept some reduction in current, you can get higher voltage from the panel:
Vmp-noct~35 volts at Imp-noct~4.18 amps... If we decrease current by ~1 amp (~29% reduction in output current), Voperating becomes ~ 41 volts (NOCT) [using Suntech's graph]:- (41v/35v) * 24 volts Vmp-noct-kyocera = ~ 28 volts (convert Suntech's Vop/Iop, because it has an I/V/P graph, to Kyocera Vop/Iop).
While that is not a high charging voltage--at (14.0 volt equivalent for a 12 volt bank)--it will charge OK. Obviously, as the battery bank becomes more charged, the final static voltage from the array (at Iop=0 amps) becomes:- (~44v/35v) * 24 volts Vmp-noct-kyocera = ~30 volts (basically Kyocera's Voc-noct)
If they were put the array in series and install an MPPT charge controller, they could get probably upwards of 40% more power from their system (as a rough guess)...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - (41v/35v) * 24 volts Vmp-noct-kyocera = ~ 28 volts (convert Suntech's Vop/Iop, because it has an I/V/P graph, to Kyocera Vop/Iop).
-
Re: Another weird setup
Thanks Bill, that makes sense.
Does the charge controller, therefore, in practice actually dictate the voltage to the panels? -
Re: Another weird setup
More or less--By the time you take heat depressing the Vmp of the solar array, voltage drop through the wiring and controller, and final charging voltage of the battery bank--Roughly Vmp~17.5 volts is the "optimum" for a PWM controller charging a 12 volt batter bank (assuming ~Vbatt-charge~14.5 volts or so). If you do all of the calculations, a hot array and cold battery bank will probably have difficulty reaching full equalization voltage--But that is probably only a limitation for the hot summer days in warm climates.
Remember, some PWM controllers can operate at higher voltages (Xantrex C40 is one)--However, your overall efficiency becomes (very roughly) 17.5 volts/Vmp-array (for a 12 volt array).
So a solar array with 40 volt Vmp charging a 12 volt battery bank on a PWM controller will have an efficiency of:- 17.5 volts / 40 volts (array) (optimum Vmp-stc for 12 volt battery charging) = 0.4375 = ~ 44% charging efficiency with "high Vmp voltage" Array and 12 volt battery on PWM controller
For MPPT, assume the same basic starting/minimum array voltage (Vmp~17.5 volts @ STC), and then the controller design allows ~40-150 VDC maximum input voltage (Voc--open circuit voltage) for most controllers... A few vendors may offer 200+ Voc operation options/configurations (Midnite Classic, Xantrex XW MPPT 600 VDC, Apollo, etc.)...
In some cases, there are also MPPT controller limitations... For example, I believe, The Outback series has an "optimum" efficiency of Vmp/Vbatt of approximately 2:1 .... If you have a Vmp-array~100 VDC and a 12 volt battery bank, the controller will tend to run warm (is that conversion efficiency issues--or just normal I2R drop and diode/switching losses--Not really sure, I don't know enough about the controller).
Check the efficiency curves for the controllers you are thinking about using... Some have better efficiency than others. And some vendors do not publish efficiency graphs, so you may need to ask.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Another weird setup
It could be that the panels are connected in series with 52Vmp ? That'll definitely charge the battery, just very wasteful of panel power.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed