Charger

Options
97TJ
97TJ Solar Expert Posts: 68 ✭✭
I see where Northern Arizona Wind & Sun recommends sizing a charger anywhere from 15% to 30% of your battery bank amp hour capacity. Reading through the forum I've seen 10% and 20% recommended. Having a 490 amp hour battery bank would a 45 amp charger be adequate? Anyone have any experience with the Power Max sold by our sponsor? Thank you in advance.

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,448 admin
    Options
    Re: Charger

    Certainly, Northern Arizona Wind & Sun has more experience than I regarding their product and solar in general. Here is my understanding/reasoning regarding my recommendations/rules of thumb:

    The 5% minimum works out fairly well as ensuring batteries are recharged in a reasonable time (if C/20 = 5%) that is about two days to recharge a battery bank that has been recharged 50%. Also, as batteries age, they tend to have faster self discharge (an old forklift battery--worst case--can be in the 1-2% rate of self discharge per day--A 5% rate of charge for 5-7 hours per day will just keep up with self discharge--Obviously getting time to replace the battery).

    10%--C/10 rate. You can recharge your 50% down battery in about a day. Also Trojan (and perhaps a couple others) recommend 10% minimum rate of charge.

    13%--~C/8 rate. For batteries in heavy industrial use (i.e., forklifts that are discharged by 80% or more per shift), C/8 is (usually) the maximum rated current without overheating the battery (or needing forced air cooling). Also, batteries are "less efficient" at charging/discharging at higher rates of charge (apparent capacity of battery bank falls with higher discharge rates).

    ~25% (or 30%?) maximum rate of charge per NAWS... From my guess, if you don't deeply deep cycle the battery bank, not huge problem with overheating. However, it would be a good idea to have a remote battery temperature sensor/monitor the battery bank to make sure everything goes as planned.

    C/2.5--C*0.40 maximum surge/discharge rate for flooded cell. I use this number as the maximum discharge rate for the "average" deep cycle battery. During discharge, if you pull more than ~C/2.5 worth of current, you run the risk of collapsing the battery voltage and not being able to (reliably) start your loads (well pump, power tool, etc.). I would guess that I would not recommend a battery charger at this current level (if the charger does not have a voltage controlled output--just current control).

    Again, just starting rules of thumbs to get us "in the ball park". If you have other needs or other than standard setup (i.e., AGM batteries--support discharge rates upwards of C*4--such as running a UPS), then we can certainly discuss and make suggestions towards optimizing the best for your needs.

    Regarding the typical 5-13% rate of charge--Another reason is to use your system to gather the most "cost effective" power... I.e., if your system recharges your battery bank to 100% by 10am every morning--You have a lot of extra solar power.

    Likewise for using an over-sized genset. Yes, you can recharge at 25-30%--but that will only be for a short period of time (during bulk phase). Once the battery reaches the "set point" (say ~14.5 volts), the "typical" charger will shift over to "absorb" charging--The actual current will begin to back down over the next 2-4 hour period (if you are going to ~95-100% state of charge). During the absorb stage, the generator begins "unloading" and running at way less than 50% of rated power output--Which, usually, is less fuel efficient.

    So, I like to recommend a smaller genset+charger rate of charge so that you can run the genset in a more fuel efficient range (>40% or so of rated output). Yes--you can run a 25+% charge rate, but you will end up using lots of extra fuel for the balance of the charging cycle.

    To see all of the factors that affect genset/charger selection, this thread has some really nice information:

    Question about battery charger selection with EU2000 generator.


    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Options
    Re: Charger

    it is also noteworthy that we speak in general terms as specifics for a battery can give rise to handle it differently than our general speak. for instance, not all agms can take high charge/discharge cycles as there are some agms by mk/decca that should only go to 30% max. always know the battery you have inside and out before you do anything. if, for instance, one were to come across a battery deal, but can't find the actual charge rate recommendations, then assume 13% max for fla and 20-25% for agm to be on the safe side. china has also jumped into the battery market making even my recommendations here as possibly too uncertain for them.