Kunfoosed is me
Highland_Fling
Highland_Fling Solar Expert Posts: 37
Charging a set of gel cell batteries from three sources Alternator Solar and Wind with them all 'active' do the three sources all charge at once? OR will because one is charging and the batteries are at 13.8V the other two controllers think/sense the batteries dont require charging OR WHAT? If they all charge at once can you explain how they do that?
thanks in anticipation
kindest regards
David
    Re: Kunfoosed is me
    In general, the charge controller set to the highest voltage "wins". Assuming all are properly connected to the battery bank (usually, not a good idea to share one wire run to multiple chargers... "Home Run" each charger directly to the battery bank).
    Note, for example, if you have a Solar and a generator setup for charging... If the generator voltage is set higher than the solar, then your generator will do most of the charging (and use more fuel).
    Your bigger issue may be that GEL batteries usually do not like very high charging currents. If you have multiple charging sources, they may add up and supply too much charging current. Check the Battery Specs and see what the proper charging current/voltage settings are for your batteries.
  • Highland_Fling
    Re: Kunfoosed is me
    OK they/are and will be all connected to the batteries by wires from their controllers
    This is on a boat :-)
    The 80A alternator is as per manufacturers wiring 100W of solar ATM going to be around 500W with a Rutland 913 wind generator
    http://www.marlec.co.uk/products/windchargers/rutland-913-windcharger/
    Yes i know Gel cells dont like masses of AMPS which is why i have not changed to a 220A alternator.
    However IF or when the Gel cells die i am thinking of changing to LifePo batteries :-) which dont have all the problems and issues with Lead Acid batteries
    BUT if the controllers all are set to 13.8 V which is i believe the recommended voltage for Gel Cells - what happens then?
    my understanding of this is a bit flaky
    Ever so slightly kunfoosed.
    The controllers wind/solar and of course my engine alternator put out something like 13.8 volts (Gel Cell batteries)
    The Batteries being at rest and at say 12.5 V are needing charged - when the (all or any of these charging sources) are charging the batteries are/is the battery voltage not sitting at (the chargers output voltage of) 13.8V with the batteries 'accepting a charge'? Fully charged and at rest voltage being somewhere around 12.5V? So until the batteries have physically reached that voltage they keep 'accepting' the charge?
    So IF one of the three possible charging sources are/is charging the batteries how do the other (one or two) charging controllers know that the batteries are indeed needing charged?
    I understand battery voltage and charge states - i think - the voltage thing that is - and i do regularly use a DVM to check on my battery charge state
    BUT surely taking my engine driven alternator our of this equation for the moment IF it is windy and sunny with both the wind and solar charging the batteries wont the batteries actually be at this 13.8 Volts level (and i believe being Gel Cells the charging voltage is held down at 13.8 V so as not to create holes in the Gel Electrolyte) so how do the wind and solar controllers know that they can charge the batteries - is it the current flow they measure....since 'surely' with either or both charging the batteries the batteries will be sitting at 13.8 V?
    Surely with solar connected and charging there will be no resting state until the batteries are fully charged................so how will the wind generator controller understand what is going on (either the alternator or the solar charging the batteries) and ADD to the battery charging. Obviously this state off affairs also relates to all charging sources and controllers - how do they know that another charging source is active and the measured battery voltage is not an at rest voltage - so the batteries (are being charged) need charging from them as well to shorten the time to fully charged?
    this is where i am very confused
    What am i missing here or what have i not understood?
    thanks again
    kindest regards
    David
    Re: Kunfoosed is me
    The controller set to 13.81 volts will "win" and the other controller set to 13.79 volts will "lose". If both are set to 13.80 volts, then they will share the current (based on their available current--alternator and solar panels, etc.).
    Charging at 13.80 volts for days/weeks on end will probably "over charge" the battery bank. So, that is why there is a "float" charge (around 13.2-13.6 volts). This is just enough voltage for the "optimum" chemistry/long life of the battery bank.
    If you "floated" the battery at 12.7 or 12.5 volts, it would not last as long and may tend to self discharge a bit (you need a "voltage gradient" to move current from the high voltage source to the low voltage destination).
    Technically, it can be a problem. Some controllers have one voltage only settings and others have absorb and float settings, along with a timer (i.e., sit at 3 hours of Absorb voltage, then fall back to float voltage until battery falls below 12.7 volts for > 10 minutes).
    Since the alternator is generally assumed to only run at limited times, it probably only has the Absorb setting (no float).
    The solar charge controller assumed to run for years, can have Absorb and Float voltage settings, plus some way to figure out the transition between the various charging stages.
    If your boat ran the diesel 24x7 for weeks at a time (motoring across the Pacific), it is possible that a high absorb only charge setting could damage the battery bank (I don't know for sure).
    More than likely, if your motor/alternator is running, it will be suppling the majority of the charging current (if all are set at 13.8 volts).
    Only when the motor is shut down, will the other charging sources start to supply more charging current (again, this depends on battery charge, your boat loads, and the settings of the charge controllers--such as 13.5 vs 13.9 volts due to wiring voltage drop and variation in calibration of the various controllers).
    Will it hurt anything--probably not unless one of your controllers is programmed incorrectly or is not functioning correctly (or you have too much voltage drop in the charger to battery bank wiring, or other issues).
    In the end, you monitor the state of charge of your battery bank (very difficult to do with sealed batteries and no battery monitor). You cannot even monitor electrolyte levels to know if you are over/undercharging.
    To a degree, people will reprogram, for example, the Absorb timer. During summer it may be set to 2 hours, and during winter to 4 hours or more (for controllers with that feature). Because, in summer, there is more than enough sun, and in winter, there is never enough.
    I hope it helps... It is confusing and, in the end, you have to monitor the state of charge of your battery bank--and adjust what you can (voltage set points, charge timers, running alternator when the battery is low and there is no sun, etc.).
    It is actually surprising (at times) that everything works as well as it does.
    But if you stop your battery state of charge vigil--At some point it will come back to bite you. It always does. :cry:
  • Highland_Fling
    Re: Kunfoosed is me
    Re: Kunfoosed is me
    I dont know how to reply to keep the format
    But here goes with my thoughts and understanding
    Well that sounds clear and understandable - so which system charges the batteries will depend on their various settings (if they are all set to 13.8V it will depend on how accurately they measure that) as well as how efficient they are in monitoring the batteries voltage.
    Surely the three controllers will ‘properly’ manage the batteries voltage and charging Plus we will be running quite a few 12V loads Refrigeration, Inverter, Lights, (LED’s) Three PC’s plus charging of phones and the PC’s and of course the Autopilot and Instruments.
    Typically the alternator will start charging at 20/30 Amps and within 30 or so minutes drop back to under 10 Amps……..this is I believe with the batteries at a 80% or so charged state and running the engine for hours and hours to get to a totally fully charged state ( the float part of the charge curve) is just silly for so many reasons………this is where I see the solar and wind coming in to play as once they are on the boat they can charge the batteries at no additional cost notwithstanding silently
    SEE ABOVE
    http://www.marlec.co.uk/products/windchargers/windcharger-controllers/
    http://www.google.co.uk/url?sa=t&rct=j&q=hrdi%20controller%20installation%20manual&source=web&cd=1&sqi=2&ved=0CB0QFjAA&url=http%3A%2F%2Fwww.jgtech.com%2Fpdf%2FHRDi%2520Manual.pdf&ei=58y6Tqe6KZT68QOynLW2Bw&usg=AFQjCNH-wyJcpawQKADakT2zWxI9LN8YuQ&sig2=Z97lguRV_K0nullZUXfdvw&cad=rja
    From elsewhere
    http://www.qsl.net/wb3gck/gel-cell.htm
    More than likely, if your motor/alternator is running, it will be supplying the majority of the charging current (if all are set at 13.8 volts).
    From reading your replies I had come to this conclusion
    NO wiring problems and issues
    We have a Merlin Battery monitor AND our Gel Cells are 11 Years old and just refuse to die
    :D:roll::blush:
    Don’t think I can re program that
    YES that was a great help as we sail in the Caribbean the days when there is no sun are quite rare - the solar is always producing something even on cloudy days.
    WE have a Morningstar 15A MPPT Controller for the two solar panels we have at the moment We might upgrade to the 45/60A MPPT Charger once we have put a lot more solar on board.
    YES 11 year old Gel Cells wooo hooooo
    __________________
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.
    many many thanks
    kindest regards
    David
