Where To Tie In
System
Posts: 2,511 admin
I'm working on a project in Central Arizona and will be connecting to APS. The project will consist of a 250 kw solar field now and another 250 kw field in the future. The problem I'm having is where to tie into the existing electrical service.
The existing main switchboard is rated 4000 amps at 120/208V, 3 phase, 4 wire. There is no main breaker but instead there are 6 disconnects. The 6 disconnects prevent me from doing a service side tap as it would be the 7th disconnect.
The ratings of the six disconnects and what they feed are as follows:
200A - elevator
200A - elevator
400A - Panel
1200A - Distribution panel inside building
1200A - Distribution panel inside building
1200A - ATS which feeds a Distribution panel in the building
The ATS is outside and near where the inverter will be located.
My question is where should I tie in? I don't want to do it at the ATS as it may violate its UL listing. Also the lugs can't handle that many conductors. Can I intercept the feed coming to the ATS and put in a new distribution board and then refeed the ATS from it as well as tie into the inverter at the new board? Any other options?
The existing main switchboard is rated 4000 amps at 120/208V, 3 phase, 4 wire. There is no main breaker but instead there are 6 disconnects. The 6 disconnects prevent me from doing a service side tap as it would be the 7th disconnect.
The ratings of the six disconnects and what they feed are as follows:
200A - elevator
200A - elevator
400A - Panel
1200A - Distribution panel inside building
1200A - Distribution panel inside building
1200A - ATS which feeds a Distribution panel in the building
The ATS is outside and near where the inverter will be located.
My question is where should I tie in? I don't want to do it at the ATS as it may violate its UL listing. Also the lugs can't handle that many conductors. Can I intercept the feed coming to the ATS and put in a new distribution board and then refeed the ATS from it as well as tie into the inverter at the new board? Any other options?
Comments
-
Re: Where To Tie In
Your Master Electrician can handle this ... 250kw system is not a DYI project
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed