6.4KW pv System 90% installed-question
Gitchee Gumee Kid
Registered Users Posts: 19 ✭
My 6.4KW pv system is about 90% installed.
Components:
30 Kyocera 215W panels ( two pole mount )
Xantrex XW6048 Inverter
Xantrex MPPT 60 ( two )
Sm battery bank -->four 200AH AGM's
8KW diesel generator 120/240 vac
Location NW Wisconsin
Question-->At a 25 % max depletion of the batteries could I power let's say a freezer thru the night?
I'm seriously thinking of going the extra mile and get 8 more batteries.
TIA
GGK
Components:
TIA
GGK
Re: 6.4KW pv System 90% installed-question
What is your daily load (Watt*Hours per day)?
We usually suggest people not get too many batteries unless they have a specific need (for example, fuel is hideously expensive and/or difficult to get to the site).
Even then, when adding "more batteries"--frequently more solar panels are needed to really recharge the bank well...
Then there is the whole cost of replacement 5-8 years or so down the line (or, heaven forbid, somebody takes out the entire battery bank a year later when some heavy loads where left on during winter).
Let's see ... 200 Amp hours @ 25% DOD is 50 Amp hours. Times 48 Volts nominally is roughly 2400 Watt hours. Or about what I use to run the whole cabin daily, including refrigerator.
That much panel would support 800 Amp hours or so of battery. -
Also, what is your peak load/surge load?
If that is a 200ah 48 volt battery bank, that would support about 2,000 watts peak and 4kW surge loads.
With a 6kW array, you should have a minimum 600ah 48 volt battery bank--otherwise you are probably going to have over voltage issues at the battery bank (I think is a F49 inverter fault)
the simple answer is yes it could power it over night and will drop the battery capacity further even though it most likely would not exceed the 50% dod point.
i would recommend 4 more batteries for as it is you are pumping quite a bit of power into those present 4 batteries at around 100a give or take. if they are concordes they can take it, but i would not be comfortable with that arrangement. any large total loads to the inverter may also bog down the batteries so that aspect has to be kept in mind too.