"No Need to Derate" What does it really mean?

bmet
Solar Expert Posts: 630 ✭✭
Is this phrase just an ad pitch? I read it occasionally, and wondered if it were written by the First Solar Salesman 60 years ago.
Comments
-
Re: "No Need to Derate" What does it really mean?Is this phrase just an ad pitch? I read it occasionally, and wondered if it were written by the First Solar Salesman 60 years ago.
Do you have a context for that? -
Re: "No Need to Derate" What does it really mean?
Found the phrase "No Need to Derate" listed for a MorningStar PWM controller on one vendor's site... And seems to be a phrase from MorningStar themselves:
http://www.google.com/search?q="No+Need+to+Derate"+site:www.morningstarcorp.com
I would guess this gets back to some definitions of how NEC rates electrical circuits and solar power systems...
Normally, you can only run a wire/circuit breaker at 80% of rated capacity.- 15 amp circuit * 0.8 = 12 amp maximum
- 20 amp circuit * 0.8 = 16 amp maximum
Also, NEC calls for "double derating" of solar panels (i.e, 0.8 * 0.8 maximum load or take the maximum Isc*1.25*1.25=1.56x; and the controller must be rated 1.56x larger than the solar array itself).
A bit of this comes from the fact that many solar products are not UL approved and the NEC is trying to fix problems by adding more "derating factors" to hardware.
NEC, from my point of view, should not be requiring deratings on solar equipment--that is the job of the manufacturer to design the product to work at "rated" loads. And, if UL approved, the controller should have been reviewed/tested/qualified by UL/NRTL's to operate at the name plate rating.
You can see if everyone keeps adding their own derating factors--you end up needing to get a ~60% large controller. And it makes the vendor's ratings sort of redeculous (i.e., the 30 amp solar charge controller can only be operated at 19.2 amps.
I would not call it a pitch--Hopefully, it is an accurate representation of the capabilities of the equipment being sold (yea--probably a bit much to hope for that).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: "No Need to Derate" What does it really mean?
Excerpt from my Xantrex C60 manual:
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 195 Solar Information links & sources, event announcements
- 892 Solar Product Reviews & Opinions
- 255 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 427 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 616 Discussion Forums/Café
- 309 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed