Panel recommendations for "48V" grid tie
Sheldon
Solar Expert Posts: 51 ✭✭✭✭
Trying to figure out what is "best" setup for adding PV to my Whisper 200 turbine.
Driving a Xantrex 4548 with a small (140AH) "48V" battery bank, running in Grid Tie where the batteries are intentionally small and used as a buffer/capacitor than for any intended storgage.
in discussion with Midnight Solar, I am of the impression that I would need only a few volts above the bank, which is set by the Xantrex setup to "sell" at 52 V.
To achieve 52V out with good efficiency in the Midnight Solar Classic, I'd need to have a temperature corrected Vmppt of the array (series/parallel) of 56-60 V.
Question: what's typical panel temperature above ambient?
I get summer temps of 40-45C peak at latitude 37, but usually accompanied by a 10-20kt North breeze at roof top, and can space array for convective venting between series panels.
I'd guess at a rise of 40-50C without explicit cooling. (contemplating a "free" pool heater by sprinkling pool water over array and catching the run off)
Assuming modest shadowing from adjacent turbine tower 3" pole (unavoidable due to zoning requirements) and guy wires, any preferred panel sizing/bypass setup?
I'd rather not provide an extra 15V at cost of another $4k row of panels, but really don't want to drop below MPPT of array on a hot day.
Driving a Xantrex 4548 with a small (140AH) "48V" battery bank, running in Grid Tie where the batteries are intentionally small and used as a buffer/capacitor than for any intended storgage.
in discussion with Midnight Solar, I am of the impression that I would need only a few volts above the bank, which is set by the Xantrex setup to "sell" at 52 V.
To achieve 52V out with good efficiency in the Midnight Solar Classic, I'd need to have a temperature corrected Vmppt of the array (series/parallel) of 56-60 V.
Question: what's typical panel temperature above ambient?
I get summer temps of 40-45C peak at latitude 37, but usually accompanied by a 10-20kt North breeze at roof top, and can space array for convective venting between series panels.
I'd guess at a rise of 40-50C without explicit cooling. (contemplating a "free" pool heater by sprinkling pool water over array and catching the run off)
Assuming modest shadowing from adjacent turbine tower 3" pole (unavoidable due to zoning requirements) and guy wires, any preferred panel sizing/bypass setup?
I'd rather not provide an extra 15V at cost of another $4k row of panels, but really don't want to drop below MPPT of array on a hot day.
Comments
-
Re: Panel recommendations for "48V" grid tieDriving a Xantrex 4548 with a small (140AH) "48V" battery bank, running in Grid Tie where the batteries are intentionally small and used as a buffer/capacitor than for any intended storage.
Depending on lots of things--You may have issues with battery bank over voltage if you feed more than 1,400 watts during Grid Tie with a 140 AH battery bank (48 volts). GT inverters cannot change the output current to the grid quickly--looks like it takes a few seconds to ramp current up and down to comply with the regulations. Just a guess, but from what I have I read around here.in discussion with Midnight Solar, I am of the impression that I would need only a few volts above the bank, which is set by the Xantrex setup to "sell" at 52 V.To achieve 52V out with good efficiency in the Midnight Solar Classic, I'd need to have a temperature corrected Vmppt of the array (series/parallel) of 56-60 V.
Question: what's typical panel temperature above ambient?I get summer temps of 40-45C peak at latitude 37, but usually accompanied by a 10-20kt North breeze at roof top, and can space array for convective venting between series panels.
I'd guess at a rise of 40-50C without explicit cooling. (contemplating a "free" pool heater by sprinkling pool water over array and catching the run off)
Given that Pmp at Vmp/max-temp curves are fairly flat, the system should work pretty well within ~10% of Pmp) even if the Vmp falls close to 60 VDC.
You still should leave a couple of volts of headroom for wiring/controller/circuit breaker voltage drop.Assuming modest shadowing from adjacent turbine tower 3" pole (unavoidable due to zoning requirements) and guy wires, any preferred panel sizing/bypass setup?I'd rather not provide an extra 15V at cost of another $4k row of panels, but really don't want to drop below MPPT of array on a hot day.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed