Off-Grid to motor
Batikikik
Solar Expert Posts: 141 ✭✭✭✭✭
Have one Berkeley motor and want to have an off-grid for it. input voltage is 240/480 3 phase and Amps: 18A . What size of system do I need and how many batteries?
Do Trojans are the best batteries??
thanks
Do Trojans are the best batteries??
thanks
Comments
-
Re: Off-Grid to motor
Trojans are probably middle of the road batteries.
Top of the line are going to be Rolls/Surrette and various industrial Forklift/Traction batteries.
Sizing the battery bank depends on two things... Watt*Hours (average watts * hours of operation per day) and maximum surge current which may be 5x the motor's full load current, or it may be much less (if using some sort of soft start motor controller like a VFD--Variable Frequency Drive).
When sizing the Inverter itself--you need to take into account not only the Watt rating, but the VA rating too... And any power factor control that may be added to the system (motor run caps, VFD's, etc.). A plain induction motor may be around 0.6-0.7 power factor, which would increase the current require by 1/0.7 or 1/0.6 times (1.43 to 1.68 increase of current).
And--What is the current rating at XXX VAC? You gave two voltages but only one phase current rating. This sounds like a 5-10 HP motor or so...
The problem with large motors running heavy loads is that it take a huge battery bank to "keep it happy"...
Lets assume that it takes 5kW and runs 8 hours a day--An 85% efficient inverter and 50% maximum discharge (lead acid battery):- 5,000 watts * 8 hours per day * 0/0.85 inverter eff * 1/0.50 maximum discharge = 94,000 WH battery bank...
- 94,000 WH / 48 volts = 1,958 AH at 48 volts
Crown Industrial Battery - 24 Volts, 1875 Amp-hours
Price: $6,892.00
Is going to cost around $14,000 just for the battery bank.
Also, remember you are going to need time to recharge the battery bank too (run 8 hours, charge for 8-16 hours) if time shifting your electrical loads.
Also, there are other losses... Battery charger will 80-90% efficient (if powered from AC mains), battery bank will be roughly 80% efficient. And you will have to replace the battery bank every XXX cycles.Specifications- 24 Volts
- 1875 Amp-hours at the 20 hour rate
- Dimensions: 38.63"L x 19.19"W x 31"H
- Weight: 2844 pounds
- 1,500 cycles / 130 cycles per year = 11.5 year cycle life?
All this is based on paper guesswork... If you need a multiple HP AC Inverter--You will need to find a company that specializes in those guys.
And, for large industrial battery installation--working with somebody who has more knowledge than I would be a big plus too...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Off-Grid to motor
Definitely looking at one MONSTER of a system that's going to require very, very deep pockets to put together!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed