How would you meter this?
ggunn
I'm working on a system with three SMA inverters on a 208V 3 phase service. Each inverter will feed a breaker contacting two of the phases. The AHJ wants metering before the interconnect; would I run the output of each SB through its own meter?
    Re: How would you meter this?
    Would you not install a 3 phase meter socket (and panel, as needed, where needed) and let the utility intall its own revenue meter? (which they may charge you for).
  • System2
    System2 Posts: 6,290 admin
    Put in a subpanel before the interconnection and output one 3 phase circuit to the interconnection point (assuming your interconnection point can have a breaker this large)
