Page 1 of 2 12 LastLast
Results 1 to 10 of 14

Thread: Maximum WEIGHT on roof ????....SOLAR PANELS

  1. #1

    Default Maximum WEIGHT on roof ????....SOLAR PANELS

    Different states , different counties , different cities has different rulesand permits regarding weight calculation on the roof .
    Los Angeles Building And Safety Department says that maximum solar panel weight you can install on the roof is 2 pounds per sq. foot.
    And different inspectors do different calculation .
    Lets say you have roof 40 feet by 18 feet = 720 sq. f.
    1- They take solar panel weight and size - lets say Canadian Solar 225watt
    Weight is about 42 pounds
    Dimensions are 5.5feet by 3.25 feet= 17 sq feet
    42 / 17 = 2.42pounds per square feet
    And after this calc they told me you cannot install . Which is not TRUE
    2 - Lets say you want to install 20 panels
    30 times 42 = 1,260 pounds
    1260/740=1,7 pounds per sq feet
    Which is more logical ....

    Who can tell acctually calc of weight on the roof ???
    I know it depends on structure and roofing material but I would like to know the RIGHT WEIGHT CALCULATION ,,,,
    Thank you guys ....

  2. #2

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    Use this document as a starting point. If you do not understand basic engineering principals hire an engineer. I went to school for a lot of years and like to get paid to figure stuff like this out.

    http://www.unirac.com/pdf/ii227.pdf
    10.125KW Netmeter System, (3) 15 panel arrays
    (45) REC225PE-US + (45) M190-72-240-S12
    SolarMount I Racking

  3. #3
    Join Date
    Apr 2007
    Location
    Lakeland Florida
    Posts
    1,959

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    There is no universal number, every structure is unique and its NOT something you can provide information on to get a permit unless you happen to be a state certified civil engineer.

  4. #4

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    I think you are asking to figure out the pounds per square foot, do you use the area covered by the panels or the area of the roof.

    Iím not an engineer, but both the load calcs I had done for my system used the area covered by the panels and included the weight of the rails. For my KD215 panels it worked out to 2.48 PSF for the panels and .5 PSF for the rails for a total of 2.98 PSF.

  5. #5

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    Source for the 2lbs/sf?

    I've been to some cities that have waived structural calcs for anything under 3lbs/sf.

  6. #6
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    10,278

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    it boils down to the inspector is right and you are wrong when he says so. too often you are under the mercy of an inspector even if you can prove him wrong, which many of them would not like especially those that are egomaniacs.
    NIEL

  7. #7
    Join Date
    Jul 2010
    Location
    Maryland Heights, MO
    Posts
    153

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    Quote Originally Posted by Batikikik View Post
    Los Angeles Building And Safety Department says that maximum solar panel weight you can install on the roof is 2 pounds per sq. foot.
    Responding to this purely from a "common sense" standpoint,
    i.e., not from rules and regulations...

    Putting aside wind load for a moment, 2 lbs per square foot is
    a rediculously low number. Think about this: if you stand on
    top of the roof, your weight is pressing on about a square foot
    (less, probably) and you may weigh 200 lbs. That means you
    have 200 lbs per square foot pressure on that portion of the
    roof, or 100 times their "maximum" solar panel weight.

    When I originally spoke with my contractor about this topic
    prior to installation, he told me that the weight of solar panels
    is a nit compared to what a roof can hold. I recall that he
    said that a roof is supposed to be capable of supporting
    something like 600 lbs per square foot.

    Now back to the wind load part. The manufacturer of my
    mounting hardware, Unirac, did run a wind load analysis to
    ensure that the proposed configuration was safe. In other
    words, static weight load is one factor, and stress load is a
    different factor and must be accounted for as well.

    John

  8. #8
    Join Date
    Sep 2006
    Location
    Willits, CA
    Posts
    5,697

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    When I did my 22 panel install in LA county, I had to have an engineer look at and certify the existing roof layout. Since it was fairly new, I still had the plans, and it went really easy, with 2x12 roof joists and earthquake sheathing (nailed every 4 inches) that were there.

    And there is a ratio between weight load and how much of the actual surface will be loaded at any point in time. if you loaded the 2nd floor of a house with the max load psf, it will fall down. That's why your foot does not go thru the roof. It's something like 30 or 40% total space loaded, not 100%.

  9. #9

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    Probably what the LA county bldg dept meant was that if you were <= 2lb/sqft you didn't need to get an engineer to sign off. It is certainly possible to construct a roof in such a way as to support more but that is not likely to be the case on the average existing residence and if you want to claim it is so you're going to need an engineer to sign off on it.

    Its not just the localized psf load... you can stand on your roof forever taking up 2sqft and thus loading it at 100psf. But fill your roof with enough other 200lb guys to use up all the other 2sqft spaces and your roof will fall down... either you will break rafters/trusses or the supporting structure will fail. You have to consider not only the load bearing capacity of the trusses but the load bearing capacity of the walls that hold up those trusses.

    Likely the more important is to consider how many linear feet of perimeter wall the roof's weight transfers to and then calculate the weight bearing capacity of those walls based on their construction (likely 2x4 stud around here). A center support beam/post/wall will likely help but there will need to be an appropriate footing or support for those too.

    And you are lucky not to have to account for live snow loads

    This is why the rules exist and why engineers get paid to do analysis.

  10. #10

    Default Re: Maximum WEIGHT on roof ????....SOLAR PANELS

    Excuse me but ... two pounds per square foot?
    That can't be right, unless you build your roofs out of cardboard and tissue paper.

    Try this: measure the square area it takes for you to stand in (approximately 1 sq. ft.). Now divide your weight by this number.

    200 lbs. per square foot I'd believe.

    Maybe you do things really differently in The States.
    1220 Watts of PV, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

Similar Threads

  1. Morningstar TS-MPPT-45 maximum number of panels I can use
    By kevinhenrycalgary in forum Solar Beginners Corner
    Replies: 14
    Last Post: March 30th, 2013, 16:53 PDT
  2. Mounting panels on an aluminum RV roof: anyone tried using a roof rack?
    By Tradiscantia in forum Solar Beginners Corner
    Replies: 2
    Last Post: March 29th, 2013, 6:02 PDT
  3. Maximum panels to add to 10kw system
    By new2solar in forum PV Installers Forum - NEC, Wiring, Installation
    Replies: 5
    Last Post: January 20th, 2012, 16:45 PST
  4. Maximum Panels for Solar Boost 50?
    By larryf in forum Solar Beginners Corner
    Replies: 6
    Last Post: August 26th, 2010, 9:01 PDT
  5. Mount my first Solar Panels on the roof - Options?
    By hunter44102 in forum General Solar Power Topics
    Replies: 8
    Last Post: March 17th, 2007, 8:20 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •