    Hello everyone,
    a quick question about inverters - can I wire up two 12V inverters to run simultaneously off my 12V battery bank? One would be on all the time (a 1000W pure sine wave) and the other I would switch on when I needed it when working in the workshop (a 2000w modified sine wave). If I wire the inverters to different terminals of the same battery bank (3 12V batts wired together) the inverters shouldn't interfere with each other?
    many thanks!
  2. #2
    Default Re: Two Inverters together?
    Providing the battery bank capacity can handle then draw off both inverters then it is oK to run them off the same DC battery bank . But keep the AC circuits separate. If you have your 3 batteries in parallel then your terminal take off should be diangonally of the first and third battery. ie +ve from battery one and -ve off battery three, tapping individual batteries paralled together is bad practice, I think Mike has a link to a good page on wiring batteries in series and parallle
    Outback FlexpowerOne FP1-6 , with Mate 3, Solar 2400W 12 x 200wp Isophoton mono Fixed Array, Tracked Single axis 972wp from 6 x 162wp Sharp Poly. Midnite Classic 150 CC. The Battery bank 12 yrs old and counting ! 700ah Exide 24 x 2v Cells, Zepher Power Vent, Midnite PV Combiner and SPD. To fit Lakota Longbow 48v Windturbine. Gesan 4.5kw 1500rpm Deutz Engined Autostart Diesel Generator.
  3. #3
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    21,981
    The other issue is when you are talking about such heavy loads (2-3 kWatts if both inverters are on an operating)--you should be looking at a 24 or 48 volt battery bank.
    A 12 volt system at 3kW would be around 300 amps or more. Heavy wire, large fuses, large switches.
    Also, Charge Controllers are rated by their maximum output current. A 60 amp controller can output ~900 watts to a 12 volt battery bank, but the same single controller will output ~3,600 watts to a 48 volt battery bank.
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.
  4. #4
    Join Date
    Sep 2006
    Location
    Willits, CA
    Posts
    5,816
    Connecting on the "diagonal" will extend the life of the batteries by helping share the loads. see : http://www.smartgauge.co.uk/batt_con.html
    What you described, if i understood it, should be good.
    Lots of batteries in parallel, is "not desirable", better to put 2, 6V in series, than 2 12V in parallel. Keep that in mind when buying the next batch of batteries.
    Attached Images Attached Images
    http://tinyurl.com/LMR-Solar
    http://tinyurl.com/LMR-BigLug
    http://tinyurl.com/LMR-NiFe
    Grundfos 10 SO5-9 with 3 wire Franklin motor (1/2hp 240V 1ph # 214505 ) on a timer for 3 hr noontime run - Runs off PV
    Powerfab poletop PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe battery | 15, Evergreen 205w "12V" PV | Midnight ePanel || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT
  5. #5
    Mike I had another look at this page from Smart Guage and he has added a fourth option for wiring up a 4 string battery bank I think its worth a look for everyone, just click on Mikes link in previous post and look at the new forth option which he claims gives perfect balance acros the 4 strings This was not on this page last year!
    Nigel
  6. #6
    Join Date
    Mar 2009
    Location
    Los Angeles, Ca.
    Posts
    1,332
    Quote Originally Posted by Johnny Portugal View Post
    Hello everyone,
    Sure, as long as the battery bank can handle the load.
    No special wiring is needed - or recommended. Just wire both inverters to the same main + and - of your battery bank. If your bank is wired properly (see above posts), then the load from both inverters will be properly distributed.
  7. #7
    Join Date
    Sep 2009
    Location
    Wilmington, Illinois
    Posts
    401
    Why use two inverters to wire one battery bank ?
    I've tried this before to get 240volts and the end result was a DEAD inverter. If you're trying to get 120 volts from each inverter to run a 240 volt circuit, STOP now !
    Both inverters are NOT in phase. Separate inverters need to communicate to sync up the phases. Once current is out of phase, will travel back to the weakest inverter and blow out the resistors. I've done this not knowing much about being "In Phase". One inverter putting out 240 volts is IN PHASE, just like the power company. When I'm talking about "In Phase" I mean that two sine waves peak at opposite sides of the zero line thus creating balance. When two sine waves are out of phase, what you just read could and can happen.
    The only way this will work is to have both inverters on isolated circuits.
  8. #8
    Quote Originally Posted by GreenPowerManiac View Post
    You're confusing the AC side of the inverters with the DC side.
    Connecting any 2 inverters' DC input to the same set of batteries is not a problem. Just fuse each inverter, and remember both are drawing off the batteries - which means even with no loads on you're feeding two inverters 'idle' current. Some people do this so they can run a small inverter with low idle current for general lighting and then only turn on the 'big' inverter when more power is needed.
    Connecting the AC side of two inverters can only be done with two matched inverters meant to be connected on the AC side: "stacked". Otherwise yes; they aren't in phase and they will fry.
    1220 Watts of PV, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.
    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps
  9. #9
    Join Date
    Mar 2009
    Location
    Los Angeles, Ca.
    Posts
    1,332
    You actually tried that? Okay...you really *are* a maniac.
    http://www.merriam-webster.com/dictionary/maniac
    "a person characterized by an inordinate or ungovernable enthusiasm for something"
  10. #10
    Join Date
    Sep 2009
    Location
    Posts
    401
    Yes, as long as both inverters run separate circuits that don't lead back to each other. And yes, both tied to the same D/C source is good, however that would be an incredible drain on 3 batteries. Running shop equipment usually draws a heavy load.
    As long as your charge rate is slightly higher than your usage, fine.
Similar Threads
  1. Inverters
    By lockwood in forum General Solar Power Topics
    Last Post: October 31st, 2012, 7:25 PDT
  2. Inverters?
    By rick3x22 in forum Solar Beginners Corner
    Last Post: May 14th, 2012, 5:42 PDT
  3. How many inverters?
    By jantje in forum Solar Beginners Corner
    Last Post: September 8th, 2011, 10:08 PDT
  4. inverters
    By ws9876 in forum Wind Power Generation
    Last Post: November 5th, 2008, 4:00 PST
  5. How about inverters......
    By pmaru77 in forum General Solar Power Topics
    Last Post: December 18th, 2006, 7:22 PST
Bookmarks
Posting Permissions
  • You may not post replies
  • You may not edit your posts