    Question Solar panel grounding

    I rejuvenate an old thread, but it never showed up in the new posts list. So I start over. It's probably redundant, but I didn't find anything else close to my question.

    I've become a pro with small wind generators, but am total nit wit with Solar. I've just ordered my first round of panels.

    Here is the question.

    What is the proper way of grounding panels?

    I am planning on bolting the panels down, using dielectric grease to some solid rails. Then I was thinking of just attaching a ground loop to each rail. Then it's to my negitive side of my buss, and earth grounds. Does this sound like a good plan? Simple and clean. Not interested in all that fancy railing. I'm already on a 45* pitch.

    Thanks in advance

  2. #2
    Join Date
    Sep 2006
    Location
    Willits, CA
    Posts
    5,714

    Default Re: Solar panel grounding

    Building Code, I believe, does not permit your version. Instead, there is supposed to be a long, continuous ground conductor, fastened to each panel, with a code approved device, at, and only at, the panel mfg's designated grounding point.

  3. #3
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    10,282

    Default Re: Solar panel grounding

    i believe they may be requiring the rails to be grounded as well, but don't quote me. i don't agree with this as the pvs will act much like a faraday shield for the rails, plus the rails are usually connected to the pvs well enough that should it (lightning, emp, or whatever) enter a rail it would transfer to the pv as the least path of resistance to ground.
    NIEL

  4. #4

    Default Re: Solar panel grounding

    I like the Tyco Solklamp product. Not cheap, but none of the approved lay-in lug devices are. Wiley ground washers are cheap but most AHJ's don't go for them.
    Why don't the module makers build in a device? I would love it if there was a built in lug inside the frame (so it doesn't stick out and get in the way).
    Putting the lugs on is always a hassle and can't be prepped ahead because you can't stack the modules once the ground lug is sticking out and also can tear into the roofing etc. I'm sure it would be a lot cheaper for the manufacturers to build it in (weld in on) and they could ensure how it is used that way. Plus the current devices do a poor job of biting through the aluminum surface to make a good gas-tight electrical connection imho.
    2.7kW Trina/Xantrex GT, 3.7kW Trina/SolarEdge, 3kW CSI/SMA GT, Solar well pump on 6, 25yr old Holeck 48W modules. Toyota SR5 converted to 108V EV. Prius w/Enginer PHEV conversion. BSEE, R11-residential, NABCEP, SunnyPro >750kW installed
    "Faced with the choice between changing one's mind and proving that there is no need to do so, almost everyone gets busy on the proof." - John Kenneth Galbraith

  5. #5

    Default Re: Solar panel grounding

    Quote Originally Posted by niel View Post
    i believe they may be requiring the rails to be grounded as well, but don't quote me. i don't agree with this as the pvs will act much like a faraday shield for the rails, plus the rails are usually connected to the pvs well enough that should it (lightning, emp, or whatever) enter a rail it would transfer to the pv as the least path of resistance to ground.
    I'm not familiar with the acumen's Niel. Forgive a rusty old man and define please? I'm a rookie on the solar side

    Thanks Guys. It's what I thought. There is no real standard. Some greedy went to the NEC and got their crap approved, raising the install costs bu tripple. There are allot easier and less expensive ways. And they wonder why more people aren't doing it.

    So far, my plan seems to be working the best

  6. #6

    Default Re: Solar panel grounding

    Only the frames & mounting parts of the panels should be grounded where the panels are mounted, for lightning protection. The negative side should NOT be grounded where the panels are mounted. The negative is usually the grounded side, but it should be grounded where it terminates - usually at the inverter for grid tie systems. (Some microinverters use a positive ground, but that does not affect the panel grounding).
    Northern Arizona Wind & Sun Forum & Website Administrator

  7. #7
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    10,282

    Default Re: Solar panel grounding

    windsun translated that as it was the mounts that i was referring to.
    NIEL

  8. #8

    Default Re: Solar panel grounding

    Quote Originally Posted by Windsun View Post
    Only the frames & mounting parts of the panels should be grounded where the panels are mounted, for lightning protection. The negative side should NOT be grounded where the panels are mounted. The negative is usually the grounded side, but it should be grounded where it terminates - usually at the inverter for grid tie systems. (Some microinverters use a positive ground, but that does not affect the panel grounding).
    Now that's a new problem for me. I have wind also which has to be earth grounded as there is no other way. Unless you think the frames and grounding the inverters is suffucient

  9. #9

    Default Re: Solar panel grounding

    The issue is not if it is earth grounded, but where. One of the biggest problems with a DC electrical ground at the panels is that you can get some really severe corrosion on any metal that touches the ground, due to it acting as one of the electrodes in the circuit. The problem is that you can end up with two different paths for the DC current - one of those through the ground, and since any metal touching the ground will act as either a cathode or anode, something will get corroded by stray DC currents. That is one of the main reasons for having a single point ground.
    Northern Arizona Wind & Sun Forum & Website Administrator

  10. #10

    Default Re: Solar panel grounding

    not all the solar panel need grounding, that dicide by the system inspection unit. somewhere will ask your system grounding.but in some special panel, just like thin-film with frame, they will ask the panel grounding for extend the life of the panel.

    skype ID:kevin_wang59

Similar Threads

  1. Aux panel frame grounding and GFDI
    By Brent in forum PV Installers Forum - NEC, Wiring, Installation
    Replies: 11
    Last Post: August 30th, 2013, 17:03 PDT
  2. Panel grounding in conduit...
    By Hairfarm in forum Solar Beginners Corner
    Replies: 20
    Last Post: March 12th, 2013, 15:47 PDT
  3. Panel Grounding
    By Joe J in forum Off Grid Solar & Battery Systems
    Replies: 11
    Last Post: November 18th, 2012, 13:35 PST
  4. Solar Panel Grounding Options
    By keyturbocars in forum PV Installers Forum - NEC, Wiring, Installation
    Replies: 1
    Last Post: April 15th, 2011, 15:07 PDT
  5. PV Panel Grounding and the NEC?
    By gregmk in forum Advanced Solar Electric Technical Forum
    Replies: 23
    Last Post: June 8th, 2008, 20:21 PDT