Re: Want to replace a damaged panel in array -- looking for electrically compatible one.
Fenachrome, OK, I apologize for attributing those errors, to you ... sorrrrry. Those specs are swapped on that SW235 data table, simply cannot be, where Vmp is higher than Voc, and Imp is higher than…1 · -
Re: Voltage where there shouldn't be any
Hi Ako, It is normal for MPPT CCs to show input voltage (on the PV terminals, and on the LCD display), in total darkness. It IS a good sign, that there is no short, to ground, from the power transist…1 · -
Re: Looking for advice: is this a fair price?
Hi (Joel, I think), welcome to the Fourm. IMO, you should get several quotes on a system that meets your needs. I assume that you are an Amateur Radio person, so, even with modern Digital modes, RFI …1 · -
Re: MX60
Jack, Here is a Link to a fairly complete MX-60 Manual: 900-0028-01-00 REV C.indd (unboundsolar.com) From the manual on Pg 48: " ... Wakeup Mode selects how often the MX60 does a “Wakeup” during…1 · -
Re: Maximum current handling from PV array
Hi Riley, You are correct, in being concerned about the Isc of the SCC. What is the manufacturer and part number of that DC-rated PV input breaker? Assume that is probably a Schneider. If you can loo…1 ·