Help for new user designing off grid power system
beto madrigal
Registered Users Posts: 2
Comments
-
How do I figure the size I need , have 11, 75w ,12v panels & 3, 120w, 12v panels & 3 , 15w, 12v panels. In total , to charge ten batteries trojan, 225ah, 6v wired to 12v , in series/parallel, have a 1500/3000 inverter, I use about 400w, an hr for about 6 day wk , about 5 hrs & what would b the best way to wire the panels
-
Beto, welcome to the forum.
I have moved your question to its own thread--Will be easier and less confusing to have the discussion focused on just your needs.
In general, I/we recommend that you define your loads first, and describe what they are. Then design a system that will (hopefully) meet your loads/power requirements. Otherwise, you can end up with a system that does not really meet your needs and/or costs more that it should.
For you--Do you already have all of the hardware? Anyway--assuming your system is somewhere in the the US southwest, and your loads are 400 Watts for 5 hours per day...
First the battery bank. For lead acid batteries 1-3 days of storage and 50% maximum discharge (for longer battery life) seems to be a "useful" range. And 2 days/50% maximum discharge usually seems to be optimum:- 400 Watts * 5 hours * 1/12 volt battery * 1/0.85 AC inverter eff * 2 days storage * 1/0.50 maximum discharge = 784 AH @ 12 volt battery bank
If you have 220 AH @ 6 volt batteries, you would need:- 784 AH / 225 AH per string = 3.5 or 4 parallel string * 2x 6 volt batteries per string
But since you already have the batteries, we recommend 5% to 13% rate of charge for solar. To properly charge such a battery bank:- 1,125 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 1,059 Watt array minimum (weekend/seasonal usage)
- 1,125 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 2,119 Watt array nominal (full time off grid)
- 1,125 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 2,754 Watt array "cost effective" maximum
Month Solar Radiation (kWh/m 2/day) 1 5.59 2 6.03 3 7.10 4 7.74 5 7.42 6 7.42 7 7.33 8 7.40 9 7.34 10 6.76 11 5.78 12 5.20 Year 6.76
Using 5.2 hours of sun minimum (lots of sun in this desert):- 400 Watts * 5 hours per day load * 1/0.52 typical off grid system eff * 1/5.2 hours of sun for December = 740 Watt array minimum
At this point, put all of the panels in parallel (you should have a combiner box with fuse/breaker per solar panel string to reduce the chance of fire if one panel gets shorted and the other feed current into the shorted cable).
You have the minimum amount of current recommended (>5% rate of charge) for your relatively large battery bank. And, if I got your location correct, because you have lots of sun in the southwestern desert--You can probably get away with a somewhat smaller solar array (5%) than I would suggest for a full time off grid system (10% or more is a typical recommendation).
The AC inverter may be a bit large for your needs (1,500 Watt for a 400 watt load)--Large inverters can have fairly high self consumption (10-20 watts+) just being turned on (tare losses). If you run the inverter 24 hours per day and it has 20 watts self consumption:- 20 Watts * 24 hours per day = 480 Watt*Hours per day of self consumption
Anyway--My first guess at your system configuration/design.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 229 Forum & Website
- 136 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 179 Solar Information links & sources, event announcements
- 892 Solar Product Reviews & Opinions
- 252 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 655 Solar Water Pumping
- 816 Wind Power Generation
- 620 Energy Use & Conservation
- 622 Discussion Forums/Café
- 316 In the Weeds--Member's Choice
- 74 Construction
- 125 New Battery Technologies
- 107 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed