More PV Math Questions

Options
StevenB
StevenB Solar Expert Posts: 71 ✭✭✭✭
OK. I've confused myself.
I want to calculate something...I'm not sure what
...but basically try to project out, based on my Pentametrix displays, how long the battery bank will maintain above 50 volts (the threshold set on the Inverter for charging), ....when it's dark or heavily cloudy..before the inverter goes into a charge cycle.

My Pentametrix reports when conditions are dark or only ambient light is on the panels, and the battery is at 51.5 volts ...it's powering the inverter with approximately 12 watts and .3 amps. The bank is (15) 12v/100ah AGM batteries.

Can someone show me the calculation, or let me know if I have enough info to project out the time until the inverter should be going into charge mode (assuming no significant sun is available?

Thanks!
Steven

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Re: More PV Math Questions
    StevenB wrote: »
    The bank is (15) 12v/100ah AGM batteries.

    I'm confused too. What kind of voltage are you running ? 180V ? An EV ?
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • BB.
    BB. Super Moderators, Administrators Posts: 33,457 admin
    Options
    Re: More PV Math Questions

    Battery voltage is not a very accurate method of measuring battery capacity if done under load (or under charge). You need to let the battery sit for a few hours (no load/no charge) to measure state of charge via voltage.

    To estimate how long until you have discharged the battery by 50% is not hard by math...

    I am not sure how 15 batteries divide evenly into a 48 volt bank... Lets assume you have 12 batteries (3 banks of 4 battery series strings). That means you have 100 Amp*Hours * 3 parallel strings = 300 Amp*Hour of storage capacity.

    300 Amp*Hours / 0.3 Amps = 1,000 Hours for 100% discharge

    Or 500 Hours for 50% discharge.

    500 Hours / 24 hours per day = 20.8 days

    At this low drain, you may end up with self discharge of your batteries leading to you having to charge them more often than just the math with the inverter...

    Also, given that batteries that sit below ~75% state of charge (for longer than hours or a day or so)--leads to sulfation which prevents the battery from properly recharging (harden sulfates do not reconvert back on recharging).

    AGM batteries have lower self discharge (and some brands say they don't sulfate down to 20% state of charge)--and may be a better solution for your needs.

    Not quite sure what your usage is (sounds like lots of battery for a very light load). Lots of batteries may need a lot of solar panels to properly charge (especially if these are flooded cells).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • StevenB
    StevenB Solar Expert Posts: 71 ✭✭✭✭
    Options
    Re: More PV Math Questions

    First, apologies...16 batteries, connected in series and parallel (4/4) ...for a 48 volt system. Slightly used, matched batch of AGM 100 ah batteries.

    Just two 60 watt Kaneka panels (in parallel), that were meant to keep the battery charged, when the wind turbine isn't producing, and wait till my budget can add more, higher watt panels and a separate high end Xantrex MPPT controller.
    Current controller is a Xantrex C40 PWA (replacing useless BZ500 MPPT).

    Xantrex 6048 inverter. Typically it uses 12 watts per hour.

    Typically the panels have been charging battery up to 52+ volts during day...by time night is starting it's usually at 51.8. I have set sell for 53.8, and because the inverter as a 1.2v threshold margin...I do sell at 52.6v. Should I set it up higher and let the battery charge higher.

    Anyway, I wanted to see what observations I could take from the Pentametrix and use to calculate a projected drop in battery charge, or identify issues with battery drop.

    I bought a desufinator, but I have to figure out how to adjust the settings properly first.

    Thanks,
    Steven
  • BB.
    BB. Super Moderators, Administrators Posts: 33,457 admin
    Options
    Re: More PV Math Questions

    Since you are grid tied--and just dealing with the inverter usage (I am not sure that 12 watts would be drawn from the battery bank when the inverter is GT connected--but SG would be a better person to answer that part of the question).

    In any case, at around 77F (standard temperature) the typical battery is 100% charged at 2.12 volts per cell (flooded cell battery). Or 50.8 volts for your bank.

    So, anything above 50.8v is "charging" the the battery (50.8+1.2=52 volts "sell voltage" for flooded cells).

    You need to look up the long term float voltage for your AGM cells (and may even want to confirm with a calibrated DVM) that you are not putting any more voltage in your standby batter bank than you need (sell mode of inverter, its backup battery charger, etc.) for normal operation (which is basically "standby"). Cycling, continuous charging, etc. will tend to age the batteries more (my humble guess).

    By the way, "Watts" already has a unit of time in it... And "Watts Per Hour" is redundant (really, it is wrong as Watts is Joules per Second--but hours are used because we would be dealing with 3,600x larger numbers for our power bills) (and yes--it is confusing, and I have made the mistake before -- because we all know Miles Per Hour).

    That amount of power 12 watts in 24 hours will use is:

    12 Watts * 24 Hours = 288 Watt*Hours or 0.288 kWH (how your home meter charges for power)

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • StevenB
    StevenB Solar Expert Posts: 71 ✭✭✭✭
    Options
    Re: More PV Math Questions

    Here's the Float Charging spec: Voltage 13.5 to 13.8 VDC/unit Average at 77°F (25°C).

    The C40 has a separate potentiometer for Float and Bulk...float is set for 53 if I remember.

    Are you saying that I should set my inverters sell down to 52 volts? That's where I originally had it, but was concerned that the batteries were not getting enough charge to sustain, under marginal conditions, enough charge to avoid the inverter unnecessarily going into a battery charging phase.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,457 admin
    Options
    Re: More PV Math Questions

    Assuming your Xantrex XW inverter is setup correctly and always in sell mode (at least when both the sun and the grid are "up")...

    Then the settings on the C40 just always need to be higher than the Inverter's Sell voltage (you don't want the inverter to be "not selling" because the "batteries are not charged" and you don't want the C40 at float because it thinks the "batteries are charged" and is cutting back on the solar array current.

    Basically, you want the C40 pouring all of the available current into the battery bank and the XW to act like a diversion load and removing all current (not needed by battery for "float") to sell.

    From what Solar Guppy (involved in the design and testing of the XW family) has recommended before (reading a bit between the lines om my part)--basically, what is the 100% charge of your AGM battery voltage (not the float charger voltage setting) and then add 1.2 volts to that--and that should be your sell voltage setting. Keeping the batteries charged and not cycling should give you the longest life.

    The batteries will remain at 100% capacity (assuming they are already charged) and virtually no energy will go into harmful reactions inside the battery (no hydrogen/oxygen gas generated, no excessive over charging current causing plate material to transfer, catalyst caps may last longer because of less H2+O2 to recombine, etc.).

    With flooded cell batteries--periodic equalization (to "boil" the cell with generated gas) to mix the electrolyte (especially on tall batteries) is still needed. For AGM, there is no mixing issues--but a very light equalization (basically maximum recommended charging voltage) once or twice a year can help equalize the state of charge between cells (most cells at 100%, a few at 5%--this appears to be a "newer" recommendation--older recommendations where to never equalize an AGM battery; which is true--you never crank up the voltage to 15.5 volts to equalize an AGM--you will generate too much gas and vent the cell).

    Clear as mud?

    -Bill

    PS: It would still be good to have the C40 set to reasonable maximum voltages--to act like a backup charge controller if the XW Inverter or the Grid goes down. More of an issue when you install a larger array.
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • StevenB
    StevenB Solar Expert Posts: 71 ✭✭✭✭
    Options
    Re: More PV Math Questions

    Yeah.
    I should ignore that info that doesn't apply to AGM's, with the exception of doing an occasional maintenance "pseudo-equalization" charge.

    I set my sell back down, not to 52v but 52.8v, since the 6048 sells 1.2v prematurely. Xantrex just issued a firmware update, so maybe that will take care of that.

    If Solar Guppy did dev work, maybe he knows a guy named Hart, who originally invented and marketed a marine inverter, and as I understand it, sold a major inverter design to Xantrex. I stumbled upon him in a remote area of Costa Rica.....a whole different potential thread I'll share if Guppy is interested.

    And back to the original question: "300 Amp*Hours / 0.3 Amps = 1,000 Hours for 100% discharge" ....So does that mean a drop from 51 volts to 50 volts is a 2% drop, and .02 x 1,000 hrs = 20 hrs?

    Thanks!
    Steven
  • BB.
    BB. Super Moderators, Administrators Posts: 33,457 admin
    Options
    Re: More PV Math Questions

    You would have to find a table for an AGM at 48 volts--but assuming the AGM is very similar to flooded cell (voltage wise)--From the Battery FAQ:
    State of Charge      12 Volt battery      Volts per Cell
    100%     12.7     2.12
    90%     12.5     2.08
    80%     12.42     2.07
    70%     12.32     2.05
    60%     12.20     2.03
    50%     12.06     2.01
    40%     11.9     1.98
    30%     11.75     1.96
    20%     11.58     1.93
    10%     11.31     1.89
    0     10.5     1.75
    
    So, a 10% drop in capacity is roughly a 0.04 volts per cell (2.12-2.08 ), times 24 cells = 0.96 volt drop from 100% charge to 90% charge (rough numbers based on flooded cell).

    I have read elsewhere here, that one of the BIG batteries (telecom or something) that the battery voltage is directly proportional to acid specific gravity. And, other than at the extreme ends of the above chart--you can see that the voltage drop is pretty much linear with decrease in stored capacity with each 10% drop in state of charge.

    So, what would I do? Not my money (;)) but--I would make sure the batteries are fully charged, inverter charger is off (it is not trickle charging at night) (and if you want to be exactly accurate disconnect one connection from a parallel string--disconnect one string so that there are no issues with restarting the inverter/charger because of no battery bank connection--but I would be just as happy to leave everything connected because a 12 watt load is almost self discharge level of loading) measure the bank resting voltage after 3 or so hours of non-operation. Then use that as your never to go below voltage (add a few 0.0x volts if you want for the 12 watt load) for your bank... And you should be sure that you are never discharging the batteries even a little bit.

    In any case, you can cycle down to 90% or even near 80% and still not damage the batteries if they stayed at those levels for long periods (days to months) of time (that I know of--I could be wrong with Lead Acid/AGM's). Obviously, that is a significant amount of sorted power "lost for use" in an emergency) by having the batteries at that low of level--but if you have solar and generator backup--it is not the end of the world.

    So, you could be down 10%@~0.96v or even down 20%@(24 cells * (2.12-2.07))=1.20 volts before I would start to worry about battery damage...

    Anyway, that gives you some pretty good numbers to play with and see how they work with your system.

    -Bill