X 5548 SW+ for Three Phase ??
Vic
Solar Expert Posts: 3,208 ✭✭✭✭
Hi All,
Have a Three Phase Genset, and now have a three phase load. Seem to remember seeing something about a 3 Phase stacking box being avail when the SW+ inverters were in production.
Have couple of systems using Trace 5548 SW+s stacked for 240 VAC -- and therefore I could come up with the third inverter. I do not have six to do native 240 VAC Three Phase, tho.
Was there ever such a device? Would it accommodate 3 ea 5548 SW+ inverters ? Guess that I would need 3 Phase transformer(s) to do 120 V in/out to 240 VAC in/out as the gensset is 240 VAC. And if it was made, does anone know where one might buy this Three Phase hardware stacker at this time ?
Called my favorite supplier, but they had not ever heard of or done 3 Phase with this hardware.
Asked this on the X Forum, but seems that the big X is too busy or uninterested to reply ... so thought I'd try here. Am off to the mountains -- no internet, so will check back in a week.
TIA for any comments, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
Re: X 5548 SW+ for Three Phase ??
I designed the original 3 phase option for the SW series sometime in the 1990's, and at that time it basically consisted of a special 3 connector cable that connected all 3 stacking connectors together, and involved one Microprocessor to be swapped out to make the phase shift 120 degrees instead of 180 degrees.
I don't remember what ever became of that... It could have probably been done with a cable that did the shifting of phase another way though... i.e., outside the SW by a separate phase shifting unit in the cable assembly. The SW+ should be similar.
Would be curious to hear what they say, if you ever do hear back on that. I kind of doubt that they would be supporting that option though.
boB -
Found this on another site a while back regarding the SW and 3phase which might be helpful.
http://www.microenergie.com/pdf/SW3Ph.pdf
FWIW I have been running Outbacks 3 phase system (3 X 3024VFX) for over 2 years and am very pleased. 3 phase loads work no problems and charging is a lot easier on the genset since all 3 phase are used.
frserapheim -
Hi boB, & frserapheim,
Just got cack to civilization.
Thank you very much for the replies. The link is very informative, but represents more hardware than I had hoped. This complexity with the additional need for Step down/up transformers twix the generator/inverters and inverters/loads seems to say that this is not the best way for me to go.
Probably should run the genset to power the 3-phase load, and use a transformer (Wye-to-Delta) between the gensset and the Inverters, and dedicated wiring between the a 3-phase load center on the genset outupt and the separate 3-phase load.
Thanks for taking the time. VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Just for the record, here is a link for the wiring of the SW stacking cable...
http://millersolar.com/resources/SWI%20Stacking%20Cable.pdf
One could create a phase shifter for this if one wanted to...
FYI, the clock lines are differential and a differential amplifier
is used internally.
boB
- 218 Forum & Website
- 647 Solar Water Pumping
- 813 Wind Power Generation
- 599 Discussion Forums/Café
- 73 Construction
