  • Re: Blown fuses

    Thanks. I will individually protect probably with inline auto-type connectors. MC4 stuff (as is most solar) in NZ is way overpriced. I just chop them off and solder. 
    ·
  • Re: Blown fuses

    The wire is 8 AWG or 8.31 sq.mm. The second question is no, the modules are wired directly into the combiner. Total combined amps is 42.3.
    ·
  • Re: Blown fuses

    The wire is 56 amp and there's about 10 foot of it. Do I need overcurrent protection? I have five panels and the largest current of any of them is 8.88A @ peak power.
    ·
  • Re: Blown fuses

    So the wire is too small, therefore I should increase the sq mm? The solution then will be to increase the amp capacity of the wire to 100, and also fit a 100 amp fuse?
    ·
  • Blown fuses

    My panels output 43 amp continuous but I've manged to blow two 50 amp fuses in as many days. This happens after a cloudy start to the day after which the clouds disappear and then very good sun. I ex…
    ·