Re: What size fuse should I attach to the positive terminals of my AGM battery bank?
Without protective covers on the terminals there's really nothing to stop a dropped non insulated tool from turning into a red hot puddle of molten metal if accidently dropped across battery ter…1 · -
Re: New Member with New system questions Magnum 4448 and Midnite 150
Are your 305 watt panels 60 or 72 cell panels? Being in the northern regions you will get cold in the winter. If your panels are 72 cell panels you may be pushing the 150 Voc. limit of your controlle…3 · -
Re: newbie looking for reassurance!
Considering the cost of a new set of batteries you really ought to consider the minor additional cost of a 40 - 45 amp MPPT charge controller. Your controller is actually limited to 20 amps, OUTPUT. …2 · -
Re: Science Fair Project
You can visually monitor the amperage of the panel with a digital voltage meter. The red lead needs to be plugged into the correct socket and the dial needs to be set to amperage. If you put the prob…1 · -
Re: Please can anyone verify my numbers
12 ga. wire should be good for a minimum of 20 amps. so not sure where the issue is. If you need to swap in 15 amp fuses you're still good to go and you shouldn't ever have any higher curre…1 ·