Re: Did I destroy my battery bank??
I suppose it may possible to build an inverter that could be field rewired to a different input voltage, but like Photowhit, I suspect it can't. The inverter appears to be out of production, so could…1 · -
Re: Mixing new with existing panel
Size of the pv string breakers is usually the max size specified by the panel maker (often 15a). You would use a wire with higher ampacity than that to minimize voltage drop. You could go as small as…1 · -
Re: Zero amps on ProStar 30
If you're going to try charging the batteries directly as suggested, a couple of things to keep in mind: - Discharge the batteries some first so there's "room" for them to take some bulk ch…1 · -
Re: Faulty Steca PR1515?
+1 on making sure to connect battery first. It appears to be a 12/24v pwm controller, and may think 24v based on pv input. It supposedly has protection for high pv input (current specs), so connectin…1 · -
Re: Very close to max wattage on my Classic 200
Going a little over 200v on a classic200 is okay. From 200 to 248v it stops charging, but lives on to charge when the voltage drops without letting the magic smoke out. As others mentioned, the class…1 ·