Re: Battery bank beginner - Stumped.
I should add... Li Ion batteries are "better" for high temperatures (>85F). And will not/should not charge if the bank is below ~40F (BMS shutdown or ruin batteries). Need to "keep …1 · -
Re: Battery bank beginner - Stumped.
The first pass answer is you can do the calculations in either Amp*Hours or Watt*Hours. Just need to know the working votlage: * 2,510 WH / 12 volts = 209 AH @ 12 volts * 2,510 WH / 120 Volts = 20.9 …1 · -
Re: 3kw Powmr 48v inverter -> transfer switch general questions
So far so good... Floating Neutral in AC inverter. If you have an backup genset--Need to confirm that it has floating Neutral (or figure out how to lift the N+G bond in genset--In theory, if you use …1 · -
Re: Amp draw for fridge - nothing is adding up
Welcome to the forum Sarah, The rating labels on appliances are (mostly) worst case numbers for a running appliance. They are not very useful for understanding/planning out a solar power system. For …2 · -
Re: Electric vehicle charging from Solar panels.
Most EV's charge from 120 or 240 VAC outlets... And normal utility power supplies 0 amps to "rated for circuit" current at a stable 120/240 VAC. Level 1 is 120 VAC at 15/20 amps (norma…1 ·