Re: Run A/C from inverter?
Given that a Honda eu2000i is supposed to be capable of starting/running a 13.5 kBtu A/C -- Especially with a good soft start conversion--It certainly sound possible. If a flooded cell lead acid batt…1 · -
Re: wiring a 24 volt system
Having the same cable lengths only matters if you have 2 or more parallel strings. A single series connected string of batteries, there is no reason to "match" battery to battery cable leng…1 · -
Re: Magnum 4448 charger/inverter
More or less, charging runs from 5% to 13% typical for solar panels. And genset charging generally runs from 10% to 20% (or even 25%)--With 13%+ rate of charge recommend having a remote battery tempe…1 · -
Re: Determining Batteries State of Charge
A couple of suggestions... First, figure out what your average load is during the day... Say it is 15 amps @ 24 volts. Then, if you are aiming for 10% rate of charge, you want the solar charger outpu…1 · -
Re: Should Negative on Battery Bank Be tied to Ground?
My humble suggestion... A properly grounded battery bank helps limit lightning damage. For AC power off grid--Our founder (now retired), in his experience, the #1 damage from lightning for off grid p…1 ·