Re: Introduction and seeking advice on 48V battery bank replacement
OK... That is better. However, the battery bank is still on the "small side" for a 3.5 kWatt AC inverter. But it does depend on how much power you really want to draw (AGM batteries can dis…1 · -
Re: Strange behavior with XW6848+ today
Not sure, but I think you need to look at the setup for your AC in section. I would be surprised if too high of input voltage did not force a transfer, just like too low of input voltage/out of speci…1 · -
Re: Ground necessary?
A "floating" power system is the "safest" type. You cannot get a "shock" from touching anything. Just like a simple battery, you touch one terminal, nothing happens... H…1 · -
Re: Strange behavior with XW6848+ today
Sounds like it is time to call the utilty and complain about high line voltage. If nothing else, you can probably get them to put a logger on your meter and get some more data. Remember too, that whe…1 · -
Re: Strange behavior with XW6848+ today
Basically, check everything from the Inverter AC1 input, back to the Meter Socket. I had one house that the neutral bus connection corroded. And another house where one of the meter socket connection…1 ·