  • Re: Strange behavior with XW6848+ today

    Not sure, but I think you need to look at the setup for your AC in section. I would be surprised if too high of input voltage did not force a transfer, just like too low of input voltage/out of speci…
    ·
  • Re: Ground necessary?

    A "floating" power system is the "safest" type. You cannot get a "shock" from touching anything. Just like a simple battery, you touch one terminal, nothing happens... H…
    ·
  • Re: Strange behavior with XW6848+ today

    Sounds like it is time to call the utilty and complain about high line voltage. If nothing else, you can probably get them to put a logger on your meter and get some more data. Remember too, that whe…
    ·
  • Re: Strange behavior with XW6848+ today

    Basically, check everything from the Inverter AC1 input, back to the Meter Socket. I had one house that the neutral bus connection corroded. And another house where one of the meter socket connection…
    ·
  • Re: Strange behavior with XW6848+ today

    Take a look at the L1 to Neutral and L2 to Neutral voltage... If you have a bad Neutral to Ground bond (typically in the main panel), you will get 120 L1 to N and L2 to N, but Lx to Ground will not b…
    ·