  • Re: Weirdest thing Ever.

    At this point, you either try to get the string of 8 working... And if they work, but don't have enough storage, just purchase one or several (AGM) batteries to get the third string working. The…
    ·
  • Re: Weirdest thing Ever.

    OK, we can estimate what the system should produce: Battery bank 12 batteries * 12 volts * 200 AH per battery = 48 volt @ 600 AH battery bank (pretty good sized). Suggest that a battery bank be desig…
    ·
  • Re: Weirdest thing Ever.

    For the battery bank, wiring can be an issue. This website has a good explanation on how to wire a battery bank so that all battery strings get equal charging/discharging current): http://www.smartga…
    ·
  • Re: Weirdest thing Ever.

    The batteries should all have pretty close to the same voltage (under charge, under discharge, resting)... Note that high voltage when charging--Probably an "open battery" (not passing curr…
    ·
  • Re: Surge Protection Devices - Single Phase and Single Pole - WHY ?

    It does depend on your local wiring standards. In North America, the neutral and green wire ground are connected together in the main panel neutral+ground bus bars. So, by itself, green wire ground a…
    ·