Re: Truth About Skystream & SWWP Gost, I am truly sorry for the problems you and your customer's have been having... Have you worked out the "real" power costs of wind vs solar PV …1 · -
Re: Truth About Skystream & SWWP
Re: Truth About Skystream & SWWP Truth Squad... Fair enough. Without knowing the number shipped, installed, and number of failures--it would be difficult for somebody who has purchased and instal…1 · -
Re: Are Lithium Batteries the way to go?
Lithium batteries are still a bit "bleeding edge". If they do not get you something, probably waiting 5 years is not a bad idea. Li Ion batteries generally have an integrated battery manage…1 · -
Re: Inverters Wired in Parallel?
Re: Inverters Wired in Parallel? One is the current at 5kW and 12 volts: * 5,000 watts * 1/10.5 volts cutoff * 1/0.80 eff * 1.25 NEC safety margin = 744 amp circuit If you are looking at running thos…1 · -
Re: Inverters Wired in Parallel?
Re: Inverters Wired in Parallel? The other question is what voltage battery bank are you looking at for 5kW of loads--hopefully 48VDC. -Bill1 ·