Re: What's best way to DOWNsize 200A load center to 150A one for a 10KW solar system install
Power harvest wise--1% is a "don't care" situation (you are doing well if you can measure your power output within 2-5% accuracy). And the variability in weather/etc. swamp any meaning…1 · -
Re: What's best way to DOWNsize 200A load center to 150A one for a 10KW solar system install
Some people oversize the inverter (for future expansion, run cooler at lower than rated power). So, if your array is only 1/2 the inverter's rating, then you would get 1/2 the rated power/curren…1 · -
Re: What's best way to DOWNsize 200A load center to 150A one for a 10KW solar system install
I do not know... Assuming a 6.4 kWatt AC inverter (and a large enough array to drive it): * 6,400 Watts * 1.25 NEC derating * 1/230 VAC nominal line voltage = 33.4 Amps minimum branch circuit rating …1 · -
Re: Is this normal for a BMK
Yes, inverters are designed to turn DC into AC power. Logging and measurements do not need to be very accurate. A precision resistor costs a fair amount 6 of money and space which is not used by many…1 · -