Re: Running a 115vac well pump, battery voltage is being pulled down tell inverter shuts off
You have AGM (sealed) batteries, so you cannot measure the specific gravity. That leaves measuring the voltage of each battery (under load, under charge, at rest) to see if you have "weak" …1 · -
Re: Step by Step Solar DIY Course for Beginners
Here is a post with a lot of solar/power books/links: http://forum.solar-electric.com/discussion/comment/99323#Comment_99323 Otherwise, you can also just discribe what your power needs are, roughly w…3 · -
Re: Enphase Inverter defective
Re: Enphase Inverter defective Can you swap the inverter with another "good one" in a different position and see what happens? That should at least satisfy you that the problem either follo…1 · -
Re: Step by Step Solar DIY Course for Beginners
From Rick at NAWS: Hey Bill, Yes, that's a book that we used to sell. We stopped carrying it 2 or 3 years ago. The book was never updated since its last edition in 2008, so I don't think I&…2 · -
Re: Battery Bank Configuration for a 48VDC, 2430 AH bank
At best in a warm climate, you will get an average of 77% or so of the 315 watt rated panels (including roughly 5% controller loss). Flooded cell batteries are around 80% discharge/charge cycle. AGM …1 ·