Re: UTILITY GRID-TIE with Back-up GENERATOR, how does it work? will it work?
The short answer is there is no "easy" way to do it. The longer answer is that newer inverters are coming out that will (probably) have "adjustable" output power. Whether this is …1 · -
Re: Could use some help with a Battery Bank/Solar setup for a food truck
Golf cart batteries are cheap because they are high volume and used many different places... The "solar batteries" are typically the same as "deep cycle batteries", sometimes opti…1 · -
Re: Wire sizing question
As long as you do not exceed the capacity/rating of the "weakest link" (the 14 awg wire in your case), then all will be fine. It is a bit unusual to mix gauges of wiring like that in standa…1 · -
Re: Wire sizing question
In general, for US/North American fuses+breakers, if you want to run a continuous 10 amps, you should increase the value by 1.25x (10 amp load * 1.25 = 12.5 amp fuse, round up to next standard size).…1 · -
Re: DC Breaker : 1Pole vs 2Pole
I would guess that, if you have a DC SPD, that you will have three wires. +/- from the battery/array and a green wire to go to ground. In theory, Array->breakers->SPD->Panel input to GT inve…1 ·