Re: One Dead Cell out of 72 - Now What
Look at the bad battery voltage string current. If the cell is open? The bad string does nothing. If the cell is shorted? The bad string is discharging the other two strings. You may be better off wi…1 · -
Re: Newbie looking for a simple solution
Be careful with the BMS assumption... Some will shut the battery off (over voltage, under voltage, over current, etc.)... Some will communicate with your controller(s)/inverters/etc. and send them th…2 · -
Re: Newbie looking for a simple solution
You need to find a Vmp ~= 35-49 VDC. Many "24 volt" panels have Vmp~30 VDC. That is too low of voltage. Vmp falls by almost 20% on hot days under full sun. Need the higher voltage to quickl…1 · -
Re: Help connecting inverter to sub panel with ATS
Big Cali, The answers really depend on the details of your needs/installation. For example, there are AC Off Grid Inverters that have their own internal transfer switch--And you can take a standard A…1 · -
Re: Newbie looking for a simple solution
OK, the min/max daily (or over night) discharge I would suggest: * 10 AH * 1/2 days storage * 0.50 max discharge = 2.5 AH @ 12 volts (2 days of storage, and less than "full discharge" of ba…1 ·