Re: Parallel with SLIGHTLY different Voltage
A 60 Cell panel would be Vmp~30 volts. Vmp-cell is roughly 0.5 volts per cell... times X cells in series gives you Vmp-panel The difference in current between Imp and Isc is something like 10% more c…1 · -
Re: Internal panel amperage
If you have a PWM charge controller, mixing 16 and 20 Volt (Vmp?) panels is not going to hurt anything. ~16 volt Vmp panels are typically 32 cell panels, not the "normal" ~18 volt Vmp 36 ce…2 · -
Re: New to solar and this site and a little problem to solve with my generator
Those appear to VAC readings, not Hz... A 1,500 or 3,000 RPM genset would have to run at ~6x normal RPM (9,000 or 18,000 RPM) to generate ~300 Hz. A 50 Hz genset running at that RPM would not be long…1 · -
Re: Is it fine to solder ferrules to wire?
The heat causing solder to melt will not be from "ambient" (room/roof/etc.) temperatures, it will be from some sort of fault condition (overcurrent, corroded connection getting hot, vibrati…1 · -
Re: Copycat
Re: Copycat Well, they are not even trying to hide the fact that these are Outback units: -Bill2 ·