Load diversion for Flex charge Controllers

daledmclean
daledmclean Registered Users Posts: 1
I have 12kw PV system using 4 outback flex charge cont for 8-820AH lead acid batteries. By 10AM at least 2 charge cont are idle. Is there some way to divert the unused power to water heating.

Comments

  • NANOcontrol
    NANOcontrol Registered Users Posts: 260 ✭✭✭
    You could consider using the ACTii controller and set it to divert when the panel voltage goes above power point.  This diverts the array voltage without using any battery.