Inverter's AC OUT to Generator Inlet Box?
TommyBoy
Registered Users Posts: 9 ✭
Hello again. As I eagerly wait for my NAWS gear to show up, I've got a question I am curious about.
I have a 30A generator outlet box outside my garage, L14-30. If I get a 2000w pure sine wave inverter with AC wiring interface, could I connect a generator cord from the Inverter's AC out to the generator inlet box to feed the main panel to run 120 stuff in the house?
I have a 30A generator outlet box outside my garage, L14-30. If I get a 2000w pure sine wave inverter with AC wiring interface, could I connect a generator cord from the Inverter's AC out to the generator inlet box to feed the main panel to run 120 stuff in the house?
Comments
-
Re: Inverter's AC OUT to Generator Inlet Box?
In theory--yes...
In practice--you have to know what you are doing and beware of some of the issues or you could start a fire.
Basically, the issue is your inverter is probably a 120 VAC sine wave inverter. And the L-14 30 plug is a 120/240 VAC plug.
Typically, what is done is that Line A and Line B are tied to the 120 VAC "Hot" output of the 120 VAC inverter and the Neutral of the plug is tied to the Inverter Neutral.
Now, 120 VAC appliances will work fine, but 240 VAC appliances will not work at all (they will see 0 volts between Line A and Line .
The danger is how the Neutral wires are run in your home... Normally with a Center Tapped 120/240 VAC split phase transformer, if you load the Line A and Line B with 120 VAC loads to neutral--the Neutral wire (return) carries no current.
However, with the Line A and Line B tied together, when you have two 120 VAC loaded Line A and Line B circuits, the return current on the Neutral (white wire) is 2x the LineA/B currents (sum of A+B current)...
So, in a home, if you have the typically Black/Red/White wiring (shared neutral), it is possible, if you have a large 120 VAC inverter, like 2,000 watts--It is possible that you could get ~17 amps (worst case) in your neutral lead (and more if >2,000 VAC inverter) and you wire it to power LineA+B with the inverter "Hot" Lead...
Will it happen--not likely (running two hair dryers on two circuits that happen to share a common neutral)... But the possibility is there.
If you get a 120/240 VAC split phase inverter setup, limit yourself to ~1,500 watt inverter, or only power 1/2 your AC loads in your house (only Line A loads, for example)--you can do it safely.
Hope that makes sense.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Inverter's AC OUT to Generator Inlet Box?In theory--yes...
In practice--you have to know what you are doing and beware of some of the issues or you could start a fire.
Basically, the issue is your inverter is probably a 120 VAC sine wave inverter. And the L-14 30 plug is a 120/240 VAC plug.
Typically, what is done is that Line A and Line B are tied to the 120 VAC "Hot" output of the 120 VAC inverter and the Neutral of the plug is tied to the Inverter Neutral.
Now, 120 VAC appliances will work fine, but 240 VAC appliances will not work at all (they will see 0 volts between Line A and Line .
The danger is how the Neutral wires are run in your home... Normally with a Center Tapped 120/240 VAC split phase transformer, if you load the Line A and Line B with 120 VAC loads to neutral--the Neutral wire (return) carries no current.
However, with the Line A and Line B tied together, when you have two 120 VAC loaded Line A and Line B circuits, the return current on the Neutral (white wire) is 2x the LineA/B currents (sum of A+B current)...
So, in a home, if you have the typically Black/Red/White wiring (shared neutral), it is possible, if you have a large 120 VAC inverter, like 2,000 watts--It is possible that you could get ~17 amps (worst case) in your neutral lead (and more if >2,000 VAC inverter) and you wire it to power LineA+B with the inverter "Hot" Lead...
Will it happen--not likely (running two hair dryers on two circuits that happen to share a common neutral)... But the possibility is there.
If you get a 120/240 VAC split phase inverter setup, limit yourself to ~1,500 watt inverter, or only power 1/2 your AC loads in your house (only Line A loads, for example)--you can do it safely.
Hope that makes sense.
-Bill
Thanks Bill, I appreciate your beautifully precise reply. Even wood-noggin tommyboy can understand that. That makes complete sense.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed