Odd issue between Generator and Inverter/Charger
TenMile
Solar Expert Posts: 62 ✭✭
So this past week, Canadian Tire had a special on Xantrex HF1000 Inverter/Charger units -- selling them at half-price for $149, so we picked one up. These units are a smart 3 stage charger that have a 20Amp charging capacity along with a built in 1000W inverter. We need a good standby battery charger once in a while, so figured this unit would do the trick and can act as a redundant inverter should the need arise.
The way this unit works once it's hooked up is as follows: when shore power is connected (via the grid or generator), the unit has a "safety" where it will not switch to shore power until it has been connected until the 20 second mark is reached. It will then pass through AC power and activate the battery charger.
Ran into a weird problem with our generator, and I am sure someone here knows the answer to what's going on. We have an older Honda generator -- an EG1400. This unit belongs to my in-laws and is well in excess of 25 years old -- however, it starts like a pro. It has a 1400W AC output and an 8Amp DC output. When I connect it to the HF1000 however, it doesn't sense the AC input when it's connected to our battery bank. I checked everything -- all wiring was correct. Connected various power tools to the AC outlet on the generator and they worked. The inverter on the HF1000 worked, but it would not detect shore power and pass it through or activate the charger. On a whim, I connected a variable-speed drill to one of the AC outlets on the generator, while at the same time I watched the panel on the HF1000 -- ran the drill at about 1/2 speed and voila -- it detected shore power and after 20 seconds, began charging.
But I can't quite make sense of this. If I connect anything to the generator, power tools, lights etc.... they all switch on immediately -- so it doesn't appear that the generator has some sort of load sensing switch. Also mentioned, that with the drill I used, I had to keep it at the "perfect" speed -- initially started full speed, but had to back it off to just below half way, otherwise, although the HF1000 sensed power it would "hiccup" in that the 20 second counter would continually reset itself if I didn't hold just the right amount of power on the drill. Anything else I connected to the generator -- various types of lights or other tools - none would allow the HF1000 to see shore power (the variable speed drill I used just happened to be the first thing I tried -- lucky).
Can anyone explain or surmise what's happening here?
Spec for the HF1000 is here: http://www.xantrex.com/documents/Inverter-Chargers/Freedom-HF/DS20080521_Freedom_HF1000-1800.pdf
The way this unit works once it's hooked up is as follows: when shore power is connected (via the grid or generator), the unit has a "safety" where it will not switch to shore power until it has been connected until the 20 second mark is reached. It will then pass through AC power and activate the battery charger.
Ran into a weird problem with our generator, and I am sure someone here knows the answer to what's going on. We have an older Honda generator -- an EG1400. This unit belongs to my in-laws and is well in excess of 25 years old -- however, it starts like a pro. It has a 1400W AC output and an 8Amp DC output. When I connect it to the HF1000 however, it doesn't sense the AC input when it's connected to our battery bank. I checked everything -- all wiring was correct. Connected various power tools to the AC outlet on the generator and they worked. The inverter on the HF1000 worked, but it would not detect shore power and pass it through or activate the charger. On a whim, I connected a variable-speed drill to one of the AC outlets on the generator, while at the same time I watched the panel on the HF1000 -- ran the drill at about 1/2 speed and voila -- it detected shore power and after 20 seconds, began charging.
But I can't quite make sense of this. If I connect anything to the generator, power tools, lights etc.... they all switch on immediately -- so it doesn't appear that the generator has some sort of load sensing switch. Also mentioned, that with the drill I used, I had to keep it at the "perfect" speed -- initially started full speed, but had to back it off to just below half way, otherwise, although the HF1000 sensed power it would "hiccup" in that the 20 second counter would continually reset itself if I didn't hold just the right amount of power on the drill. Anything else I connected to the generator -- various types of lights or other tools - none would allow the HF1000 to see shore power (the variable speed drill I used just happened to be the first thing I tried -- lucky).
Can anyone explain or surmise what's happening here?
Spec for the HF1000 is here: http://www.xantrex.com/documents/Inverter-Chargers/Freedom-HF/DS20080521_Freedom_HF1000-1800.pdf
Comments
-
Re: Odd issue between Generator and Inverter/Charger
Ah crap -- I think I see the problem myself.
After reading the Xantrex spec on the unit -- the shore power relay is 30Amps. Doesn't tell you that in the manual -- just in the spec sheet I just posted! -
Re: Odd issue between Generator and Inverter/Charger
Terry;
The 30 Amp rating on the transfer switch means it will handle loads up to 30 Amps. It should detect and switch regardless of power demands. It's possible the problem is the generator's frequency is off - running a bit high until you put a load on the generator and slow it down a bit, bringing the frequency with range that the Xantrex can work with.
Time to buy a new Honda EU2000i! -
Re: Odd issue between Generator and Inverter/Charger
...or a different charger
So you're thinking that our generating is producing something beyond 60Hz? -
Re: Odd issue between Generator and Inverter/Charger...or a different charger
So you're thinking that our generating is producing something beyond 60Hz?
This is a standard generator. Its output frequency is dependent on the engine RPM. Normally they do run a bit fast, because when the load is applied they instantly slow down a bit. There's a compromise between frequency and RPM and load capacity. With no load the engine may run 3780 RPM's and the frequency may be as high as 63 Hz. Put a load on of at least "X" Amps and it pulls down to 3600 RPM and 60 Hz. At that level it can handle loads up to a certain level before the engine starts to slow and the frequency goes down.
Pretty much typical of the beast. :cool:
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed