SunPower SPR-95: maximum string length?
A first post from The Netherlands, Europe.
I'm about to buy a couple of SunPower SPR-95 panels because of their high efficiency and the limit space I have available to mount them. A datasheet of those panels can be found here:
http://www.solarenergy-shop.ch/Datenblaetter/Sunpower%20SPR-90%20Photovoltaik.pdf
The idea is to connect those panels to a Mastervolt Soladin 600 inverter whose datasheet can be found here:
http://www.sunstore.co.uk/csi/92667904/f/pdf/soladin_600_data.pdf
According to my calculations, one should minimally connect 3 SPR-95 panels in series to meet the lower range of the MPP window, even on hot days assuming the start-up power of 1W@40V DC is always easily reached.
Also, a maximum of 6 panels can be connected, although the panels might deliver more than 600W on some occasions. The inverter will never feed-in more than 600W into the grid.
However, the dealer got a reply from the German importer of those panels (apparently, SunPower has them made in China) stating that one is not allowed to connect more than 4 SPR-95 panels in series.
Assuming that the answer of the importer is independent of the inverter applied, my question is why can one not make a string of 6 SPR-95 panels in series and connect them to the Soladin 600?
Thanks in advance for any feedback!
Hieronymous
Hieronymous
Re: SunPower SPR-95: maximum string length?
From what I can (and cannot) see... My guess is the 95 watt solar panels have a "low" circuit voltage rating... In the US, we rate our "standard" line voltage components for 600 VAC maximum. In Europe, I have seen some 1,000 VAC ratings.
The Sunpower does not list their rated voltage either, but it could be as low as 70 VDC... Voc=21.5, so:- 4xVoc=86 volts
- 86 volts * 1.25 typical NEC derating = 107 VDC
- 107 VDC * 1/sqrt of 2 (DC to AC peak voltage conversion) = 76 VAC rating
Just a guess--You should call/email them and ask what their maximum system voltage rating is. The typical solar panel specifications should read something like:- Framed modules certified by TÜV Rheinland as Safety Class II (IEC 60364) equipment for use in systems up to 1000 VDC
- Framed modules listed by Underwriter’s Laboratories for electrical and fire safety (Class C fire rating)
- 600V (IEC 61215 rating)
There is a TUV and UL rating for the SunPower Panel:TUV-R: IEC 61215, Safety Class II Certified
UL Listed: UL 1703, Class C Fire Rating
I don't know the IEC / UL numbers -- So I don't know if IEC 61215 is a 1,000 Volt rating or if there are other allowed ratings...
Bill,
Thank you for your quick reply.
1. I did some more digging to find the maximum voltage rating ("maximale Systemspannung" in German) of the SPR-95 panel as you suggested in your post but it is hard to find.
This first link below states it is only 70VDC (you're a pretty good guesser ), while the other mentions 120V (guess DC too) for the older SPR-90 panel (datasheet from 2004):
http://www.solarenergy-shop.ch/index.php?cat=KAT17&lang=DEU&product=P0158
http://www.solarlink.de/PDF-Files/Sunpower/SPR-90_de.pdf
It seems that I still have to check with the importer to know what the exact value is.
2. From your post, I now understand that the maximum voltage rating is determined by the isolation and cell backing. I'm a bit surprised that it is so low. Do you have any idea why it is so low? Other, more powerful, SunPower panels are rated for 1000VDC.
3. I don't exactly understand how a single panel in a string of for example 6 panels, clearly exceeding the rating in your example of 80VAC, can be damaged by overvoltage. Where, or how i.e. in which circumstances, can a too high voltage drop arise in one of the panels of this 6 panel example leading to permanent damage?
4. From the IEC 61215 documentation, I understand that it is about standardized testing methods independent of a panel's actual maximum system voltage. It only states how this should be tested.
Thanks again for any feedback.
Hieronymous -
Re: SunPower SPR-95: maximum string length?Hieronymous wrote: »2. From your post, I now understand that the maximum voltage rating is determined by the isolation [should be insulation] and cell backing. I'm a bit surprised that it is so low. Do you have any idea why it is so low? Other, more powerful, SunPower panels are rated for 1000VDC.3. I don't exactly understand how a single panel in a string of for example 6 panels, clearly exceeding the rating in your example of 80VAC, can be damaged by overvoltage. Where, or how i.e. in which circumstances, can a too high voltage drop arise in one of the panels of this 6 panel example leading to permanent damage?
Normal electric code (US) basically uses 600 VAC as the minimum safety design for our 120/240 VAC (or higher) electrical systems. The testing of appliances (and wire insulation) is (as I recall) done at 3xRated voltage--Or in this case 1,800 VAC (we can also pass the test with sqrt of 2 x 1,800 volts--typically used when our equipment had Radio Frequency grounding capacitors--No AC 50/60 Hz leakage currents).
So--In this case, either the panels were never designed to take 1,800 VAC production tests, or there could be "insulation punch through" to the metal frame and/or through the backing... Or, they simply never tested to 600 VAC and bothered getting the UL/TUV/CSA/NRTL listings for that high of voltage.4. From the IEC 61215 documentation, I understand that it is about standardized testing methods independent of a panel's actual maximum system voltage. It only states how this should be tested.
Will the panels system work OK at your 155 Volt system maximum (or less, because you only want 6x panels in series)... Probably--They should have been tested at 3x70v=210VAC (or VDC). (This is a common mode test--i.e., one lead of XX votlage from the tester to attached to "both +/-" leads; and the second tester lead to Panel Metal (aluminum frame, possibly some sheet metal/mesh to the real of the unit) to look for that failure (arc, leakage current, etc.).
However, it is a (small?) gamble. Solar panels are mounted outside in wind/sun/hot/cold/rain/salt air/dust/dirt/etc... I have no way of establishing if there would be a hazard or not. And, I don't have any information on the connection box (or pig tail wires) as to what voltage/application they were designed to support.
Sort of the equivalent of using 12 volt wiring and switches for cars to wire your home... Not usually a good idea.