    Coming late to the dance, but here is my two cents,,,

    I have a lttiile frigidaire 5k BTU unit I run very rarely. I run it on my eu1000 Honda genny. I sue the slow start method, run the engine on full throttle, no load, turn the fn on and let it spool if full for a few minutes, then turn the compressor on low. The Eu100 will barely start it,, but runs it fine. It draws ~550 wats running.

    My guess is that you are going to be REALLY hard pressed to get any meaningful run time off nearly any 12 v battery set up. Even if it would run it, my guess is that any inverter will drop out due to low voltge shut down first. You could start it on the genny, and the a quick switch to the battery while the compressor is still running, then leave it running full bore so the compressor never shuts off.

    Tony
    Please note, being a moderator does not add any weight to my opinions 300 watts Siemens/BP panels,plus a Sun 90,, making ~400. ~30 amps into Rogue MPT-3024, 450 ah of Trojan T-105, Morningstar ts300 inverter, a Tri-Metric meter.a collection of antique generators, plus 2 Honda eu-1000i's (also a BS2512 IX controller) and assorted other stuff!

  2. #22
    Join Date
    Apr 2012
    Location
    Van Horn, TX (West TX)
    Posts
    611

    Default Re: Air Conditioner 5-6K on 1000 Watt Inverter..

    Photowhit..

    Thanks.. for clarifying..
    I found some locally available Grape Solar 190 Watt Monocrystalline panels rated at 5.25AMP and 36.2V DC.. @ $290/each..

    That also clears up the battery issue.. (I confuse easy).. so realistically I should have 2 banks of 4 (total 8*6v) and then I would be 400ah rated in total.. hypathetcially I could run my AC for like 3 hours and be about +75% left in the bank..
    Last edited by ywhic; April 14th, 2012 at 5:34 PDT.
    Al Z.
    1160 watts PV, 30.86 & -104.792, MidNite Classic 150, Xantrex Pro SW 2000, TS 30 Transfer Switch

  3. #23
    Join Date
    Apr 2011
    Location
    Everson Washington
    Posts
    155

    Default Re: Air Conditioner 5-6K on 1000 Watt Inverter..

    I would go with the swamp cooler in a heartbeat, we used one in
    colorado and could drop the temp from 80 to 69 degrees in about two hours in a 2000 SQ Ft. home. I wish I could run one in the NW. I would plan at least 2000 watt inverter 24 volt MIN.(with a good surge rateing) and plan on running off PV ,not batteries.....I am going to try this also but havent upgraded my inverter yet.
    Off grid in the NorthWest looking for the sun

    4.8 KW PV with growing pains/500W turbine feeding C60 & dump loads/ 3 XW MPPT60's/cotek S1500 1-24/cotek S150 1-24 /cotek sk3000-124 TriMetric 2025/700AH 24v

  4. #24
    Join Date
    Apr 2011
    Location
    Everson Washington
    Posts
    155

    Default Re: Air Conditioner 5-6K on 1000 Watt Inverter..

    The newer swamp coolers dont use that much water, in our town in Gunnison Colorado water was like Gold. You learned not to waste a drop, and we did OK......Our well was 285ft down and another 100 ft. to our three story house
    coming from the mid-west this was a culture shock.....
    Off grid in the NorthWest looking for the sun

    4.8 KW PV with growing pains/500W turbine feeding C60 & dump loads/ 3 XW MPPT60's/cotek S1500 1-24/cotek S150 1-24 /cotek sk3000-124 TriMetric 2025/700AH 24v

  5. #25

    Default Re: Air Conditioner 5-6K on 1000 Watt Inverter..

    Quote Originally Posted by ywhic View Post
    That also clears up the battery issue.. (I confuse easy).. so realistically I should have 2 banks of 4 (total 8*6v) and then I would be 400ah rated in total.. hypathetcially I could run my AC for like 3 hours and be about +75% left in the bank..
    Right battery bank, but you'll need a minimum of 1000 watt array (panels) to support it.
    Home system- 20 - 200W Evergreen blems, 2 Classic Lites, E-Panel, 2 Prosine 1800 watt inverters, 800AH 24V forklift Batt, up and running 1 Classic Lite and 14 Suntech 185W in spare room.
    Experience with Pulse/Trace PC250 Power Center, Original Rouge CC, 80-4/5watt 6v panels, Odds and extras,

  6. #26

    Default Re: Air Conditioner 5-6K on 1000 Watt Inverter..

    I'm in hot/humid FL. Swamp coolers don't work here. So when the grid goes down, I drag out a 5000 BTU A/C unit. To make sure it works with my hardware, I did some testing.



    First wanted to make sure it worked with a Yamaha EF2400iS generator.

    With the fan on high, and the compressor engaged, draws almost 5A. It's rated at 600W, so the numbers are close.



    After a few minutes I shut it off, then immediately tried restarting it. This is the worst case scenario, and not what you should do. Restarting too fast can stall the compressor as the pressure in the system is still maxed. Ideally, you should wait several minutes, allowing the pressure to drop. This isn't an issue when allowed to cycle normally. I wanted to challenge the generator.



    This tiny A/C pulled over 18 AMPS starting current! My generator momentarily picked up RPMs, then dropped back to an idle.

    The Xantrex Prosine 1800W inverter performed equally, if not better.

    My intent is to use my 900AH battery bank at night for the A/C unit, and critical loads (fridge, some lights, small TV, computer, etc), and a combination of a 1000W solar array, and the generator with a 75A Iota charger, to replenish the energy used at night.

    I had no problem cooling the master bedroom, bathroom, and short hallway with this A/C unit during the middle of Summer when the central A/C failed. After ~20 minutes, the room cooled down and the compressor cycled off. The blower only draws 0.2A.

    I also agree a 1000W inverter wouldn't likely start it, or at least not restart it when there's a head pressure.

    If swamp coolers work in your area, great! If not, it's still possible to use a window shaker.
    Robert
    Central FL
    http://www.2manytoyz.com
    900W of solar panels, 860 AH 12V battery bank (8 6V Golf Cart Batts), Xantrex Prosine 1800W inverter, Xantrex Prowatt SW2000 inverter, 2 Prostar 30M controllers, 1 Morningstar Sunlight 10L controller, Iota 75A charger (for rainy days), Furrion 30A automatic transfer switch, Yamaha EF2400iS generator.

  7. #27
    Join Date
    May 2010
    Location
    Desert Southwest, USA
    Posts
    38

    Default Re: Air Conditioner 5-6K on 1000 Watt Inverter..

    I've found that these window A/C's burn a little more juice after they've been running a while, than when they first start.

    If you have water, definitely go with an evaporative cooler!

    Example: It turned unusually hot here (103 F). And with my setup (see sig) I could barely run one 5k and one 6k BTU A/C's between 10:30 am and 2:30 pm with no other loads. And even then, I was pulling 1 to 2 amps from the batteries in addition to what the panels were putting out. Granted, compressors were running constantly, non stop...
    OB Flexware 500, 3648 inverter, two FM60 cc, eighteen Kyocera 135sx panels, sixteen Lifeline 105Ah 12v AGM batteries - off grid. (grid power available) 6800w diesel gen

Similar Threads

  1. Propane heaters will not run on Honda EU2000 or Cotek st-1000 inverter
    By Basicplus in forum Off Grid Solar & Battery Systems
    Replies: 27
    Last Post: May 7th, 2014, 10:43 PDT
  2. CNC Machined 1000 Watt Wind Turbine
    By mroy0404 in forum Wind Power Generation
    Replies: 5
    Last Post: June 23rd, 2012, 10:22 PDT
  3. 1000 watt turbine near completion.
    By old wind in forum Wind Power Generation
    Replies: 0
    Last Post: November 27th, 2011, 15:24 PST
  4. Inverter 458 COMBI & Link 1000 Monitor
    By Jim45D in forum General Solar Power Topics
    Replies: 3
    Last Post: November 2nd, 2011, 21:50 PDT
  5. Xantrex Freedom HF 1000 Inverter/Charger
    By lotwsolar in forum Advanced Solar Electric Technical Forum
    Replies: 12
    Last Post: July 13th, 2011, 20:23 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •