changing power , do i need 1-O-2 switch
prince_77
Solar Expert Posts: 31 ✭
Hi all
i have 2 power, one is offgrif and one regualr, i want to transfer the power from the regular side to the offgrif side and i understand that i can use 1-O-2 but i think i dont allow to share the neutral wire from both system
so i need a 1-O-2 that also cut the neutral wire and switch it also?
where can i find something like that
thanks
thanks
The simplest method is to use the transfer relay built in to most Power Inverters,
My Inverters all have an AC input for utility power, A DC input for Battery power, and then the AC OUTput to the load panel.
Alternately, you can use a DPDT power relay, or a manual transfer switch, like THIS:
http://www.homedepot.com/h_d1/N-5yc1v/R-202495852/h_d2/ProductDisplay?selectedCatgry=SEARCH+ALL&jspStoreDir=hdus&catalogId=10053&navFlow=3&keyword=88322&Ntpc=1&langId=-1&Nu=P_PARENT_ID&storeId=10051&Ntpr=1&ddkey=Search -
Re: changing power , do i need 1-O-2 switch
You are proposing using an AC transfer switch to change some loads between utility power and inverter power (as would be the case for emergency back-up for instance). The unit Fullpower linked to is a good choice for this.
What you have to watch out for is not the neutral lines, but the neutral-ground bond which will exist somewhere in the system. Two things to be sure of there: A). that there is only one such connection in the whole system; . that there is no such connection present anywhere in the wiring if connected to an MSW type inverter. A true sine inverter will not be a problem.
Also as Fullpower mentioned, if you're using a large inverter/charger unit they have automatic transfer switches built-in: if they detect AC IN is "live" they will switch their output loads to that and begin charging the batteries from the AC source.