AGM Battery Desulfator

huntep
huntep Registered Users Posts: 9 ✭✭
I just acquired four AGM NSB-170Ah telecoms batteries which were being replaced... I have them connected to my charge controller XW mppt60-150 which seem to do a good job of charging them up. However, I was wondering if the controller acts as a desulfator or should I equalize them or what?. They dont seem to stay up very long. The current setting for the charge is AGM and 3stg. bulk, abs, float...

Thanks for allowing my post.. Very interesting forum. Keep up the good work.
BTW I have hybrid XW4024 with 6X195 Sun panels and XWMPPT60-150 Charge cntrl.

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Re: AGM Battery Desulfator

    I'd suggest you try a couple 80% charge/discharg cycles, to "open up" the plates that have sat in float for 5 years.

    Also, they are likely disposing of batteries that are 5 years into their 7 year life, and may not have much left in them. What was their voltage when you got them ? If much under 12.5V, they are likely toast.

    AGM should not never, ever be equalized, unless you have specific instruction from the Mfg on how to do it, and how to monitor and measure the process. DONT DO IT !
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • waynefromnscanada
    waynefromnscanada Solar Expert Posts: 3,009 ✭✭✭✭
    Re: AGM Battery Desulfator

    mike90045 said it better than I could have. Totally agree with him.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    Re: AGM Battery Desulfator

    Here is a thread how one company (Concorde) recommends to "recover" their AGMs... Not supposed to apply to any other brands of AGMs:

    Sulfated Lifeline Concorde AGM Batteries

    And here is a great thread from DapDan with information on how one place recommends to restore AGM batteries (new catalyst caps, adding water to cell, etc.):

    Low rest voltage on GNB absolyte IIP cells

    In the end, trying to do "extreme" things to batteries should be done in a safe area and always under some sort of supervision/monitoring (don't want to overheat the cells and blow acid around) and performed while wearing appropriate safety gear/gloves/face shield/water/hose/baking soda nearby/etc.).

    And--if the cells are otherwise scrap--if you can try some of the above things (if done safely)--you are not loosing much anyway.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Re: AGM Battery Desulfator

    "They dont seem to stay up very long."

    what exactly do you mean by this? give detail.
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Re: AGM Battery Desulfator

    re "They don't seem to stay up very long."

    you also need to test them as per the manufactures load testing procedure, usually a 20% of rated capacity, and record the results to compare against the Manufacturers tables. This will help in assessing battery health...

    Eric
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • huntep
    huntep Registered Users Posts: 9 ✭✭
    Re: AGM Battery Desulfator

    Thanks everyone for your input.. I found the problem, one battery had a hairline crack on the side and caused the bank to fail prematurely.i.e. after about two hours. AGM dont leak even with a crack...(12 batteries in series/parallel 24v) system. I can run all night now after replacing it.
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Re: AGM Battery Desulfator

    here is some condensed info I received from an AGM servicing company a while ago, you may find helpful.