    Interested in using this for my off grid cabin - does anyone know which would be best? have 1500gal tank that we use for rainwater harvesting - need decent pressure to the cabin / garden

  2. #2

    Default Re: Shurflo Pump?

    So no need for lift, just pressurizing lines? What power do you have available? They make 12 VDC, 24 VDC, and 120 VAC models. The basic 12 Volt is a little over $100.
    1220 Watts of PV, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #3

    Default Re: Shurflo Pump?

    just need pressure - tank is little above the cabin - still debating on 12-24v system

  4. #4
    Join Date
    Jul 2007
    Location
    Quetico, Ontario
    Posts
    5,025

    Default Re: Shurflo Pump?

    Actually, most of the shurflos are good pumps in my experience

    I would consider this one for full time:

    http://legacy.shurflo.com/pages/RV/r...r/extreme.html

    tony
    Please note, being a moderator does not add any weight to my opinions 300 watts Siemens/BP panels,plus a Sun 90,, making ~400. ~30 amps into Rogue MPT-3024, 450 ah of Trojan T-105, Morningstar ts300 inverter, a Tri-Metric meter.a collection of antique generators, plus 2 Honda eu-1000i's (also a BS2512 IX controller) and assorted other stuff!

  5. #5
    Join Date
    Aug 2010
    Location
    New Zealand North island
    Posts
    194

    Default Re: Shurflo Pump?

    Have one running for 5 years now to a header tank about 10 meters head . Hasn't missed a beat.
    I'm on 1 2volts but would definitely go for 24 if starting again.

  6. #6

    Default Re: Shurflo Pump?

    Thanks for the information, last ? How to add it to 24v system if I decide to go that route

  7. #7

    Default Re: Shurflo Pump?

    Quote Originally Posted by Jcrabtree View Post
    Thanks for the information, last ? How to add it to 24v system if I decide to go that route
    24 Volts worth of battery and a charging system to match?
    Sorry, but not knowing what you've got now or how much the pump will be used it's hard to be specific. Could you elaborate?
    1220 Watts of PV, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  8. #8

    Default Re: Shurflo Pump?

    nothing yet - still up for debate 12v - 24v system wanted to start off small with rogue charge controller available in June - 4 T105re batteries - panels still up for debate - as for watts/amp - per day still in the works.

  9. #9

    Default Re: Shurflo Pump?

    Just as a sample based on four 225 Amp hour 6 Volt batteries:

    112 Amp hours (50% DOD) @ 24 Volts = 2688 Watt hours power potential
    22.5 Amps @ 28.8 Volts charging = 648 Watts, less typical 77% derating = 842 Watt array
    Quick AC potential estimate: 1684 Watt hours per day.

    Could be better, could be worse.

    The ol' 12 vs. 24 question still comes down to what you expect to have in sustained loads: 1 kW or less, 12 Volts will do. Over that and 24 becomes attractive.

    Were it not for the pumps needed at my locale I would have stuck with 12 Volts - and a much smaller inverter. Skip the electric 'frige too, and I could have used the Morningstar 300. Although that didn't exist at the time.
    1220 Watts of PV, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  10. #10
    Join Date
    Apr 2010
    Location
    Pescadero BCS
    Posts
    100

    Default Re: Shurflo Pump?

    I highly recommend the variable speed DC pumps for domestic water. They don't cycle on and off when you barely crack open a faucet, just run slower. I'm using the Jabsco version, the only problem that I've found with it is that sometimes the over voltage protection in it will shut it down for 5 or 10 minutes right before my batteries go to float.(any suggestions?) It works well with the demand heater, the heater doesn't shut off if someone opens a faucet somewhere else.

Similar Threads

  1. Problem with Shurflo pump
    By lazza in forum Solar Water Pumping
    Replies: 9
    Last Post: August 1st, 2013, 10:36 PDT
  2. Using Panels directly to 12V Shurflo pump
    By lazza in forum Solar Water Pumping
    Replies: 12
    Last Post: May 29th, 2013, 9:16 PDT
  3. Solar power for Shurflo pump?
    By DevanW in forum Solar Water Pumping
    Replies: 2
    Last Post: January 19th, 2012, 10:47 PST
  4. shurflo pump 115 volt model
    By bobdog in forum Off Grid Solar & Battery Systems
    Replies: 0
    Last Post: March 27th, 2011, 19:41 PDT
  5. Shurflo vs Conergy pump
    By gpigeon in forum Solar Water Pumping
    Replies: 10
    Last Post: June 20th, 2007, 3:54 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •