Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
mcnutt13579 said: I did what you suggested.....tried to start it without gas as you said it would crank for 15-30 seconds. It did not. It cranked for 3 seconds then gave the LR code. I just posted my…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
mcnutt13579 ok, I did what you suggested: I completely SHUT OFF the propane, pushed the run button, and it cranked for 3 seconds and gave the LR error code. It did not act like you said it would. I h…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
The propane feed was at 10.5" at the solenoid inlet, and dropped down to 9.5" upon the generator starting. The propane was adjusted up to 14" and dropped down to 13" upon the gene…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
Aguarancher: Thanks for the info. I confirmed with my propane supplier rep this morning that 3 lbs psi of air probably would have damaged the generator regulator. He is coming to the house this Thurs…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
mike95490 thanks....I will stick to 3 lbs then...not sure how gravity feed would work to check for leaks but I know pressurizing the line should work...3 lbs at say 6 pm, 1 lb at say 10 pm, leak.....…1 ·