Re: Generator on the fritz
Original problem was occasional shut down, charge controller showed low voltage fault. I checked connections,etc. Then a few weeks later, gen would crank up, begin to run for a split second then imme…1 · -
Re: Gen low voltage
Thank you,What a great forum. I will do some re-torquing today.Merry Christmas1 · -
Re: Gen low voltage
New info. I poked around in the settings and found that the inverter will accept 80v to 150v from the gen. When under load the gen is showing 117.5 on average. So seems like I don't need to adjust an…1 · -
Re: Gen low voltage
Will be at the site tomorrow and will post voltage not under load.1 · -
Re: Gen low voltage
Good Question. Unfortunately the Sunny Island inverter only accepts 120. I was not too knowledgeable when I bought the Kohler. I was concerned about the potential imbalance, but it never seemed to be…1 ·