Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
You shut off the propane after you had it running a while? So that it would have otherwise started? Or was this for the first start of the day when it always has the problem? What about warranty cov…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
Even if you completely SHUT OFF the propane, if it is behaving correctly it will crank for something like 15-30 seconds and then cool the starter down. Then recycle a couple more times before it give…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
About 95% certain the LOCKED ROTOR code CANNOT be set by a start-then-die problem. That would result in a different code, something like loss of speed or loss of RPM. LOCKED ROTOR is when it checks f…1 · -
Re: Kohler 14 RES Generator Locker Rotor: Continuous Issue
The 14RESA (that's what it really is, right?) gets its speed (engine rotation) sensing from the auxiliary windings (55 and 66). Basically it is just sensing ac power which is kind of marginal at cran…1 · -
Re: Blown fuses
For the record, it is allowable to combine 2 strings into one set of conductors without breakers or fuses. Reason being, any short in solar module leads will be carrying 21 amps in from one direction…1 ·